Hello people ,looking for some help with this query, Have just started work (as a mate) for a water company . On their pumping stations (the green boxes you see) they appear to have a spike and a tncs system- is this allowed or normal for some installations? or have i missed something ? I ll get a picture and put it on next week so you can see for yourselves .It is to be part of our initial survey .

thanks
 
Originally TT, changed to TNC-S by DNO, nobody took the spike out, that happens a lot.
 
TNC-S should be max 0.35 ohms and the spike, well anyones guess but not highly unlikely to affect the TNC-S reading.

Disconect the earth conductor as normal and test the TNC-S Ze and see what you get. If you confirm that there is a TNC-S supply then disconnect the TT, confirm that you have that Ze before you disconnect anything.
 
adviseable . to eliminate parallel paths and confirm that you have TNC-S. either way, you should get a reading of <0.35
 
Last edited:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Spike and t-n-cs ?
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
jules27,
Last reply from
telectrix,
Replies
4
Views
1,158

Advert