Hi all,

I am having a new summerhouse built at the end of my garden circa 50m from house consumer unit. House has TNCS earthing arrangement. I was planning to run a 10mm 2 core SWA cable to the summerhouse and put in an earthing rod and earth direct to that. Someone has just advised to run a 3 core and connect to house earthing. Which is the best option. Obviously would i would get a professional to connect etc but was going to do the majority of the cable runs etc myself. Need to run the cable before summerhouse is built S currently having a patio laid and cable will run under it.

please could someone advise which is the best and safest method.

many thanks in advance.
b
 
depending on the loading, 10mm might be big enough, but it might not.
I would suggest running a duct so the cable can be pulled through later.
it is often worth pulling a couple of network cables down at the same time.
cctv, wifi, bird box camera etc.
 
depending on the loading, 10mm might be big enough, but it might not.
I would suggest running a duct so the cable can be pulled through later.
it is often worth pulling a couple of network cables down at the same time.
cctv, wifi, bird box camera etc.

Thanks James, good idea with network cable.10mm 2 core has a rating of circa 80a. I thought that would be sufficient. It’s for a fridge, tv, small electric heater, a few sockets and lighting. May later run a 13a hot tub off the summerhouse CU at a later date. Just confused about best earthing method to go with as two people have said two different methods. With one saying I could not earth off the house TNCS.
 
perfectly OK to use the house earthing. run a 3 core SWA. 10mm should be protected with a fuse/MCB of 50A.
 
at that distance, around 30A is the most you can push down 10mm and stay within 3% volt drop.
hot tub and heater combined could be 26A so it is not as much spare to play with as you might think.

Agree with @telectrix about the earthing arrangement.
 
at that distance, around 30A is the most you can push down 10mm and stay within 3% volt drop.
hot tub and heater combined could be 26A so it is not as much spare to play with as you might think.

Agree with @telectrix about the earthing arrangement.

Thanks everyone. So would you recommend 16mm SWA just to be safe?
[automerge]1597339775[/automerge]
Thanks everyone. So would you recommend 16mm SWA just to be safe?
Just found the guys message he sent regarding earthing, saying that if it’s for a hot tub or running water then i can't export TNCS earthing system to man cave from house.
 
Last edited:
cost difference is likely to be negligible in the scheme of things.
so bigger is better as they say.

I would recommend that you get the spark that will finally connect it to specify the cable type and size, route, method of burial, depth, marker tape etc. all agreed before purchasing anything.
 
Thanks James, good idea with network cable.10mm 2 core has a rating of circa 80a. I thought that would be sufficient.
Just confused about best earthing method to go with as two people have said two different methods. With one saying I could not earth off the house TNCS.

You've missed some steps in your calculation if you managed to calculate that 10mm can carry 80Amps at a distance of 50metres!
At a guess 10mm might be OK for 32A at that distance.

Whoever told you you cannot use a TNCS earth to an outbuilding was talking nonsense.
[automerge]1597340244[/automerge]
Thanks everyone. So would you recommend 16mm SWA just to be safe?
[automerge]1597339775[/automerge]

Just found the guys message he sent regarding earthing, saying that if it’s for a hot tub or running water then i can't export TNCS earthing system to man cave from house.

No, I'd recommend carrying out the cable size calculation and volt drop calculation to work out what size cable is required.

It would be nice to hear the reasoning behind that statement about hot tubs and running water, I doubt very much they can support the statement with any regulation.

If a 3 core cable is used with a CSA of 10mm or greater then it will satisfy the requirements for main bonding and allow the use of the TNCS earth.
 
i'd use 10mm with up to 40A load. this would give a VD of 9V @ 40A over 50m, which is over the 3% for lighting, but that 3% came from the days where incandescent and fluirescent lighting was the norm. with LED lighting it's out of date. tin hat firmly attached to bone head.
 
Really all that matters is that the voltage is sufficient for the current operating equipment Such as led drivers which normally state an operating voltage of between 220-250 volts.
The 3 percent is a safe design value, the voltage could be around 245 volts say before you’ve even installed a sub main.
Then again it could be less.
 
Hi all,

I am having a new summerhouse built at the end of my garden circa 50m from house consumer unit. House has TNCS earthing arrangement. I was planning to run a 10mm 2 core SWA cable to the summerhouse and put in an earthing rod and earth direct to that. Someone has just advised to run a 3 core and connect to house earthing. Which is the best option. Obviously would i would get a professional to connect etc but was going to do the majority of the cable runs etc myself. Need to run the cable before summerhouse is built S currently having a patio laid and cable will run under it.

please could someone advise which is the best and safest method.

many thanks in advance.
b

I would just like to thank everyone for their help, support and advice. It is greatly appreciated.
 
Not sure of actual figures but I think the CSA of the SWA of a 2core 10sqmm is greater than 10sqmm equivalent copper and can therefore be used as a TNCS bonding conductor.
 
Not sure of actual figures but I think the CSA of the SWA of a 2core 10sqmm is greater than 10sqmm equivalent copper and can therefore be used as a TNCS bonding conductor.

The armour of a 10mm 2 core SWA cannot be used as a 10mm binding conductor, it isn't big enough.
You cannot directly compare the CSA of the steel armour with the required CSA of the copper because the conductivity of steel is approximately 8 times lower than that of copper so you need a steel CSA of approximately 80mm to be used in place of a copper 10mm bonding conductor.
 

Reply to Summerhouse earthing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
535
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
854
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
  • Locked
My house was built in the 1930s, The fuse in my service cut out is 60Amp and the wire coming from the street has a 16mm2 copper core(easy to see...
Replies
12
Views
572

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock