J

johntom

Hi
just wanted to check something with you guys.
If you tested R1 + R2 on seperate a 6a lighting circuit with just selv downlighters (using a temp link in the cu), where would you take the reading from ?
 
Same as always at the furthest point.

If there are many downlights throughout the building i expect the circuits will be terminated at the switches, which would make things a little easier.

Good luck!
 
hi jontom are you asking because of the selv fittings because the cpcs should be continuos to( as jason and lenny said the furthest point) try to find last transformer
 
Hi
yes because of the transformers, presumably you would you have to test at the end of the T&E (instead of the normal cpc / switch live inside the ceiling rose) otherwise no cpc / R2 in the downlighter fitting from the transformer?
 
yep wherever you think the last point is remember all mains circs should carry cpc
 
hi i always test at the last light ( furthest point ) there is nothing wrong in testing at the switch
in the new gn3 it shows ( R1+R2) being taken from the switch
 
Testing at the last point is fine, if you only have single points in each room, But when you come to Spots you need to prove that each Spot circuit has earth to the end of its run, So in effect, test at the very last point of the circuit, but if another room has downlighters in you should also test at the last point in that downlight set up. Doe's that make sense??


Im effect when fitting downlighter in multiple rooms Your Spurring off a Radial circuit, So CPC should be checked at the end of each 'spur'.
 
  • Useful
Reactions: 1 person
Hi
do you test the end of the T&E as there wouldn't be a cpc from the transformer to the downlighters (so you can't test R2 by removing the bulbs) ?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Testing continuity with downlighters
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
johntom,
Last reply from
Spudnik,
Replies
10
Views
5,095

Advert