each circuit will have it's own value of Zs depending on the resistance of the cable, so you have to measure each circuit. look at the schedule of tests. values of each circuit need to be recorded.
The Zs measurement at the furthest point on each circuit should be recorded.
By measuring Zs at each point on each circuit, you will be able to prove continuity of the CPC, and polarity of any switches.
Reply to testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...