I rather foolishly booked in a fault finding job in a 2 hour slot thinking I could solve it quickly, I couldn't!

It has me confused, although I haven't let myself slow down yet and focus so you guys may point out something obvious.

It is an intermittent tripping MCB on a 32A ring ciruit (sometimes the RCD trips) on a dual RCD board. It trips a number of times each day. This has been going on for perhaps a week. Over the last 2 days 5 sockets have actually stopped working completely even with the power on. The ring feeds the whole house.

r1 = 0.14 Mohm (140,000 ohms)
r2 = 28K ohms (28,000 ohms)
rn = 0.7 ohms

With all sockets connected and the ring split in the CU I get :

Leg 1 = L/N - E 0.01Mohms
Leg 2 = I didn't write down the results but they were >1Mohm.

When I split the ring at one socket the IR results were all >1Mohm when tested in the CU, I didn't test at the split socket.

I think I'm getting confused because of the 5 non working sockets. If a ring is broken (as this is) all sockets should still work. Am I right in thinking there HAS to be 2 faults either side of those non working sockets (assuming they are not all spurred from the same socket) or am I missing something?

Usually, in order to find the break I would split the ring. Reconnect the leg that has continuity with the relevant leg in the CU liven them up and eliminate the working ones, but if there are 2 breaks this wont work, i don't think!

Update... the customer has literally just rang saying he removed a socket and just plastered in the cables a while ago and when he bangs that part of the wall it trips! However, this would be just one fault and would still not stop 5 sockets from working!! o_O :disappointed::anguished::tired:
 
Last edited:
I rather foolishly booked in a fault finding job in a 2 hour slot thinking I could solve it quickly, I couldn't!

It has me confused, although I haven't let myself slow down yet and focus so you guys may point out something obvious.

It is an intermittent tripping MCB on a 32A ring ciruit (sometimes the RCD trips) on a dual RCD board. It trips a number of times each day. This has been going on for perhaps a week. Over the last 2 days 5 sockets have actually stopped working completely even with the power on. The ring feeds the whole house.

r1 = 0.14 Mohm (140,000 ohms)
r2 = 28K ohms (28,000 ohms)
rn = 0.7 ohms

With all sockets connected and the ring split in the CU I get :

Leg 1 = L/N - E 0.01Mohms
Leg 2 = I didn't write down the results but they were >1Mohm.

When I split the ring at one socket the IR results were all >1Mohm when tested in the CU, I didn't test at the split socket.

I think I'm getting confused because of the 5 non working sockets. If a ring is broken (as this is) all sockets should still work. Am I right in thinking there HAS to be 2 faults either side of those non working sockets (assuming they are not all spurred from the same socket) or am I missing something?

Usually, in order to find the break I would split the ring. Reconnect the leg that has continuity with the relevant leg in the CU liven them up and eliminate the working ones, but if there are 2 breaks this wont work, i don't think!

Update... the customer has literally just rang saying he plastered in some cables a while ago and when he bangs that part of the wall it trips! However, this would be just one fault and would still not stop 5 sockets from working!! o_O :disappointed::anguished::tired:
You need to start from scratch in your testing procedure. let nothing distract you, finish testing and analyse the results.
 
and when he bangs that part of the wall it trips!


oh my .... good luck with this one. Rather you than me.

seriously though. Remove every socket. Check what’s in the rfc and what’s spurred off.
buzz every leg so you know what goes where.
I had one fault finding mission turned out to be a faulty socket. Ie, all my cable testing was clear, but tripped rcd when I put the faceplates back on.
 
first dig out his bodge and clear that fault. thenlogically test for the other fault/s. split ring and get wander lead out. i like to go round with wander lead on the socket screws before lifting sockets. increasing values as you get further from CU. once the layout is found, then start on the fault/s.
 
ring a ring of roses ,start one end and till you have found it .split it half and a quarter and see what you get ,a bright spark for doing the job right .I had one the other day a faulty rfc it was the first leg that went to the first socket ,other sockets where ok .
 
Weird duplicate post, see below!
 
Last edited:
One break could well be a badly made joint where he has plastered the cables into the wall (assuming there must have been some attempt to join them to give the rn continuity). If the failed sockets had some significant loading between them, then another weaker joint may have since failed due to increased loading after the socket removal.

If the plaster is still wet, that could also be the source of the low IR. Sounds like thats a good place to start, but as others have said you will probably need to map the whole ring to check for extra spurs and interconnects etc.
 
There must be:
No breaks in N (you have end-end continuity)
At least 1 break in CPC (no end-end continuity, but might be present at all sockets)
At least 2 breaks in L (not present at all sockets)
By break, I'm talking about a defective connection or severed conductor that might have very variable resistance.

The intermittent short / flashover that is responsible for the MCB and RCD tripping is presumably under the bit of wall he bangs, and it is probably also the site of one of the breaks. You can read the resulting defective insulation on leg 1, as 0.01MΩ, and should be able to read some kind of defective IR on leg 2 albeit with up to 0.14MΩ end-end resistance in series. However, mashed cable faults and loose terminals are sufficiently unstable that I would not set too much store by the fact that you got a reading >1MΩ on leg 2 instead of 0.14MΩ at the moment you tested it.

Crack on...
 
faulty edit being fixed now
Thats a pity as I was about to quote you...

In your final paragraph you wrote something along the lines of... "whilst on one leg the fault cannot be seen". My 11 year old son happened to be reading it and decided to stand on one leg, he fell over crashing into the cat which sprang up onto a shelf sending everything flying, he then fell on to the floor in a laughing frenzy!

Thankyou Lucien :D
 
Thanks for the replies everyone. I think (as most of you have said) that I will find one of the faults clear when I break into the wall and fix his plastered in socket. I can then hopefully start some more 'standard' fault finding with only one fault left to find.
 
Thanks for the replies everyone. I think (as most of you have said) that I will find one of the faults clear when I break into the wall and fix his plastered in socket. I can then hopefully start some more 'standard' fault finding with only one fault left to find.
Looking forward to the updates...(with pictures....no pressure !)
 
Isn't it great after hours of head scratching when the customer just happens to mention/remember things like this.... :rolleyes:
On fault finding I listen to what they say but never believe them to be giving me all of the information...
Me: "What where you doing when the RCD tripped? Any cooking, put the kettle on, ironing etc"
Customer: "Nothing just watching TV"
Me: Plugs kettle in, switch on, trips. Tests kettle, L-E short.
Customer: "Oh yeah forgot it happened as I turned kettle on"
:weary:

More difficult fault here but the most important bit of information needed was left out.
 
Update....

I returned this morning at 8am. It turns out the customer hadn't hidden a socket in the wall, they had removed a TV wall bracket and plastered over. I cut a hole in the wall (stud wall) where the bracket had been and found this..

Above socket.jpg close up.jpg

I fixed the above which cleared the poor IR results and got the 5 non working sockets working, I then started fault finding the broken ring. I'd already quizzed the customer a number of times about any thing they'd done or anything out of the ordinary. 30 mins into the fault finding they remembered they'd had a spark off a redundant fused spur. I opened it up and found a disconnected line and cpc. Connected them up and the ring tested as intact.

Then.... I tested the RCD (as at the beginning it was not tripping when tested which I thought may be due to the fault(s) as this sometimes stops the RCD from working) with all outgoing terminals disconnected (thanks again DS). It was faulty. I put a new one in, all tested fine!

3 major faults! Bloody ell, never had that before. I am now having a half day off so I can sit contentedly with a superior grin on my face whilst sipping my coffee and telling you all about it ?:D
 
Result. There's nothing better than using skill and strategy to solve a problem that started out so obtuse that it was difficult even to describe to begin with.
 

Reply to This fault has me confused! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
472
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
447
I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
255
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock