Discuss three phase rcd in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi guys.
Can anyone explain in simple-ish terms how a three phase rcd measures a currents imbalance? It can't be between phases as not all three phase systems are balanced equally so it must be between phase and neutral big how?
Just curious!
It measures the same as you would clamp a 3 phase circuit with your earth leakage clamp meter to test for leakage. If it's 3 phase no neutral then the sum of all the currents flowing simultaneously in the 3 phases will equal zero if there's no leakage. Likewise with a 3 phase and neutral circuit except the neutral current must also be included in the zero sum equation.
Current in will always equal current out.
interesting if its not a balanced load then it will need a neutral so yes any in balance between line and neutral would trip the rcd but im interested myself to here other peoples versions of how a balanced load with no neutral would trip the rcd
exactly equal currents in each phase means the the current in the neutral is Zero
marvo if say there was 10amp on each phase so 30 amp total how would this equal zero ive had this explained to me a while ago but scratching head trying to remember lol
Because the voltage phase angles of each phase are 120 degrees apart so when current is flowing one direction in one of the phases it's flowing in the opposite direction in at least one of the other phases.
Current flow in a circuit is a physical thing like water flow in a pipe, an Amp by definition is a Coulomb of electrons flowing past a point in one second and a Coulomb is an actual number of electrons. You can picture an Amp of current flow as being similar in nature to a litre per second of water flow in a plumbing circuit so if a quantity of electrons (current) is flowing one direction in one leg of a circuit an equal quantity of electrons (current) has to be flowing out of the circuit.
An RCD can theoretically work on any number of conductors, so long as every conductor in the circuit has its own sensing winding on the RCD transformer. A single-phase RCD has two windings, a 3-phase has four, you could make one with six windings for 5-phase power!
Farm, visualise a 3-cylinder radial aero engine, with all three con-rods sharing a crankpin. The positions of the pistons represent the currents / voltages on a balanced 3-phase system - the moving mass of each piston is balanced by the sum of movements of the other two.
thanks marvo wow your first explanation was easier ha ha cheers
Lol, I'm trying to keep it simple, honest.
If you understand how a single phase RCD works then you should be able to get how a 3-phase RCD does. It's basically a current transformer where current through the circuit conductors all cancel each other out so they balance which means that no current is induced into the sensing winding. It's only when there's leakage to earth that they no longer balance and it's this imbalance that causes a current in the sensing winding which in turn operates the mechanism that causes disconnect.
My tradesman got caught out by one of these the other week. Scratching his head why the 30A 3-phase drives were running fine but a piddly little burner tripped the 200A main switch every time. Turns out another worker had left the neutral out of the main RCD.
Reply to three phase rcd in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
TT system, existing three phase fuse board recently installed by another spark which only has single phase circuits terminated into individual...
4K
