If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Hello,

I've been asked to install a supply for a TP air source heat pump to heat a swimming pool.

The pool room CU is feed from a barn with a TP supply and luckily the SWA feeding the pool room CU is a 4 core.

The barn is going to be converted in the near future into 2 holiday lets so I'm going to upgrade the ancient board that's in there.

My question is can I cover the couple of SWA submains by a 30 or 100ma time delayed RCD and have it conform? I have hardly touched any TT systems as we don't have many around where I am.

Many Thanks.
 
Time delayed 100ma S type are usually a main switch with a split load board of maybe 2 30 ma RCDs to give you discrimination. What is the type of supply at the origin. Is the ground condition suitable to drive in a Earth Electrode, may be test the soil resistance first if you can The issue I think you may have is the inrush currents of the heat pump unless it has a soft start built in. Rcd’s don’t usually like high start up currents. The heat source pump Would need to be protected by a 30 mA Rcd .
There is bound to be other guys replying once the pubs turn out .
 
Last edited:
At the source I have a 3 phase TT incomer supplying a 3 phase board. There's 3 sub mains from that board to the pool house, tennis court and garden room.

My plan is to upgrade the 3 phase board in the barn using a 4 pole 100ma time delayed RCD as the main switch to cover the 2 SWA sub mains and then 30ma RCBO the barn finals. Then have a 1 way three phase board in the pool house for the pump.
 
  • Like
Reactions: pc1966
At the source I have a 3 phase TT incomer supplying a 3 phase board. There's 3 sub mains from that board to the pool house, tennis court and garden room.

My plan is to upgrade the 3 phase board in the barn using a 4 pole 100ma time delayed RCD as the main switch to cover the 2 SWA sub mains and then 30ma RCBO the barn finals. Then have a 1 way three phase board in the pool house for the pump.
Your Plan sounds okay to me as long as you get a low enough Earth Electrode resistance. I think you may need to check with the Pump Manufacturer as to what 3-phase RCBO or RCD they may specify. C type etc. They will know the expected inrush current.
 
  • Like
Reactions: pc1966
Both 100mA and 30mA RCDs should have rod impedances less than 200 ohms (for evidence of stability of earthing, not the 500ohm/1.67k that 50V/In gives) and that is normally OK to meet with a single rod.

But check any existing rods for both soundness of connections and their Ra.
 
  • Like
Reactions: Electro-tech

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Hampshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
TT Submains time delayed
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Clinchy,
Last reply from
pc1966,
Replies
4
Views
1,342

Advert