M
mickeymarrow
Hello All,
I am a new member with a question i hope you can help me with.
TT System, Ze test with main earth disconnected from earth bar reading = 195 ohms
Zs test on ring main reading = 0.68 ohms..!
Retested Ze but this time connected to the earth bar (main earth not connected to earth bar) = 0.15 ohms...!
Tested again, this time with gas and water bonding disconnected reading again = 0.15 ohms...!!
Question is, can parallel paths bring the value down by this degree or is this potentially a major issue?
Mickeymarrow
Parallel paths through connected equipment in contact with extraneous conductive parts....immersion heater,boiler...etc.
Hello All,
Mickeymarrow
This is absolutely normal on a TT installation, as Wirepuller said, parallel paths nearly always pull the Zs at the DB way down from the Ra value of the earth electrode.
TT System
Thread Tags
mickeymarrow,
IQ Electrical,