Discuss very low pfc on submain board in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

L

lucus

hi all hoprfully someone here can answer this question for me: i tested a sub mains today and i only got 0.35 KA is this normal for a submains as at the main mainsboard the pfc is 3.3 KA the main fuseboard has a rcd main switch so at the submain i had to use no trip pfc not sure is this makes and difference any imput would be great.
regards
 
Did you test Zs at sub main and if so what was this reading.
 
Hi Lucus

What was your Zs at the sub main ? It will be higher than at the origin so therfore the PFC will be lower.

So as long as all protective devices throughout the installation have a breaking capacity equal to or more than the origin main protective device,then recording the origin PFC is good enough.

Mark
 
That PFC would be for a Zs at the board at around 0.65 ohms. So not sure where you're going wrong there.... You should be getting a PFC of around 0.68kA if all correct.
 

Reply to very low pfc on submain board in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
613
Hi, I have a project I have been working on, that has me out of my depth with regard to my knowledge, as I am a very basic electronic hobbies...
Replies
5
Views
1K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock