Hi,

I need to take a Supply from a house CU to an outbuilding which has a 20A radial socket circuit and 6A lighting. The cable run to the outbuilding is 20M then the lighting circuit inside the outbuilding is approx 10M in length and the socket cicuit 15M in length.

I'm trying to calculate a suitable size cable to be feed via a 32A mcb in the house.

Taking volt drop into account so that the full 32A can be utilised i have calculated that.

6mm feed 7.3 x 32 x 20 / 1000 = 4.67v
---------

1.5mm lighting circuit 29 x 6 x 10 / 1000 = 1.74v ------- > 1.74v + 4.67v = 6.41v < 3% 6.9v (ok)
-------- ---------
2.5mm socket circuit 18 x 20 x 15 / 1000 = 5.4v -------- > 5.4v + 4.67v = 10v < 5% 11.5v (ok)
------- ---------

so a 6mm 2 core swa would be suitable to supply this installation

Does this look good to you?

Thanks
 
without double checking your sums, that looks spot on to me, although i don't think you'll pull more than a couple of amps on the lighting, meaning that you're on the right side.
 
Excellent,

The house earth type is tn-s, there's potentially a 2 steel roof brace that could be earthed. I was planning on installing an Earth rod to make it a TT system. what do you think?
 
use the TN-S. 3 core SWA and earth the armour both ends. as for the roof brace. determine if it's extraneous by testing to earth on 500V IR. if the reading is above 22k, ignore it. is there a water service into the outbuilding?
 
ok good thanks! From what i can see there used to be a service from a pvc pipe that's got a tap on the end, i presume it's been turned off at a stop cock before entering the building as nothing comes out the tap. There's no internal plumbing and no plans for it in the near future (being used as an office) so i guess i'm safe with exporting tn-s from the house.
 

Reply to volt drop in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi, I'm looking for a bit of advice on a volt drop query we have in our office. I'll explain the scenario and I would really appreciate any...
Replies
3
Views
618
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Why is this still a thing, just done a quick calculation with the TLC volt drop calculator and if its a non lighting circuit the recommended size...
Replies
3
Views
910
Domestic property Supply number 1 6 flood lights 4x400watt= 1600 watts 250meters from board to closets corner of tennis courts Tennis court...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock