6.9 v for lighting
11.5 for a socket.

So my question is to calculate the size of a supply cable to a building that had lighting power heating for example. What figure would i use for voltage drop.

Is there a wxtra safe rule of thumb method ppl use?
 
id use the 11.5v mate. its not just sockets its everything other than lights. to the best of my limited knowledge the vd limits are because light fittings some times have voltage sensitive equipment.
 
6.9 v for lighting
11.5 for a socket.

So my question is to calculate the size of a supply cable to a building that had lighting power heating for example. What figure would i use for voltage drop.

Is there a wxtra safe rule of thumb method ppl use?

If the sub main has both lighting and power as final circuits then you need to use the figure of 6.9V or 3%. This has to be the maximum volt drop from the origin to the last point on the lighting circuit.
 
Voltage drop is monitored to ensure that loads are not deprived of too much of their operating voltage due to cable resistance.

Each final circuit will be treated independently, whilst distribution circuits may need further consideration.
 

Reply to voltage drop. in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
729
Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Replies
5
Views
2K
Why is this still a thing, just done a quick calculation with the TLC volt drop calculator and if its a non lighting circuit the recommended size...
Replies
3
Views
910
I am sending power to some 5v led lights about 50ft from the transformer. I was going to use some CAT6 direct Burial cable that I kept after a...
Replies
2
Views
1K
Hi, I'm looking for a bit of advice on a volt drop query we have in our office. I'll explain the scenario and I would really appreciate any...
Replies
3
Views
619

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock