This is in conjunction with an EICR I have just carried out.
9.5kW shower on 6mm and 32A MCB. Been in place for a long time, no signs of thermal damage in CU or 45A shower pull switch. Ref method C (where visible in loft), unable to clarify ref method where it is buried in walls, but no conduit visible. My thoughts.... No code, but I am unsure of the effect of 41A going through a 32A MCB over a long period of time? Will this eventually damage the MCB or have some other effect on it that may compromise it's ability to work as it should, and if so, is this a very unlikely occurrence that doesn't really need to be considered or the opposite?
No 30mA RCD on cable <50mm in walls (for 3 x circuits... cooker, water heater, lights).
No 30mA RCD for circuits running through/in special location
Main bonding in place, nothing to supplementary bond.
My thoughts.. I have always put C3. I still think C3, but I am starting to err towards C2 in general for no RCD. This is for 2 reasons, RCD's are now required for pretty much everything (and they save lives), secondly, does anyone know what the NAPIT codebreakers says about no RCD protection? I believe they say C2?
Cheers all.