HappyHippyDad

-
Esteemed
Arms
Reaction score
5,294
Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

I have just (kind of) completed an EICR. It was the worst house I have ever been in. They are horders plus the house was filthy. I was unable to get to certain areas.

I realise there are a number of fails (c2's) with the picture but my question is regarding the 2 x 10mm tails coming out of the cutout and going to 2 way consumer unit. They are both neutrals.

One of these goes to the neutral bar in the consumer unit and one goes to the main switch in the small CU.

I haven't seen a neutral go straight from the cutout to CU before. From looking on line it seems that this is ok. Is it? The one neutral going straight to the neutral bar means the main switch is not isolating the neutral. I feel this should just be removed? Pictures below..

What is going on with this cut out and the neutrals. Cut out - EletriciansForums.net What is going on with this cut out and the neutrals. scan - EletriciansForums.net
 

snowhead

-
Mentor
Esteemed
Arms
Reaction score
5,497
Where the small C.U sits on the backboard there are old screw holes around it and more in other places around the backboard and above.
It may have had an Off peak setup with separate timeswitch and meter.

But I'd say that someone somehow ended up with a Neutral or 2 left over still sealed in the cut-out and thought I'll just park the spare Neutral in the small C.U.
The seal fairies were probaby on holiday that day and couldn't attend.

Can't blame the "Smart" boys and girls this time, it predates them.
 

brianmoooore

-
Esteemed
Arms
Reaction score
5,411
Main switch in both CUs isolates line and neutral. The oddity in this setup is that the neutral to the second CU does not go through the link bar in the meter.
I have come across setups like this before, where the neutral in the cutout has one wire to the meter and one wire direct to the CU, and I've wired a few private meters like this.
 
OP
HappyHippyDad

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,294
Where the small C.U sits on the backboard there are old screw holes around it and more in other places around the backboard and above.
It may have had an Off peak setup with separate timeswitch and meter.

But I'd say that someone somehow ended up with a Neutral or 2 left over still sealed in the cut-out and thought I'll just park the spare Neutral in the small C.U.
The seal fairies were probaby on holiday that day and couldn't attend.

Can't blame the "Smart" boys and girls this time, it predates them.
I think you're probably spot on there. Well noticed with the screw holes!

They had night storage heaters removed many years ago.
 

Gavin John Hyde

-
Esteemed
Arms
Patron
Reaction score
5,149
Will you be wanting the DNO out to pull fuse etc to sort the tails or will seal fairy be on call?
With the looped supply it does complicate things a bit I guess but If you tell WPD that you will be 'fitting ev charger' in next few months they will unloop the supply and give you a nice new cut out free of charge! may dig the customers garden up though!
I did read something once about some looped service heads where even though house a has its fuse removed you can still get some quite high currents on the neutral and earth if PME/bonded via the looped supply as these are not meant to be fused but will likely share the same terminal in the service head before going off to house b
 

ipf

-
Mentor
Esteemed
Arms
Reaction score
6,733
Something like...a bit.
Two CU's, two Henleys. The live Henley is on the outgoer from the meter, the neutral Henley is before the meter, resulting in one CU neutral bypassing the meter.
Back at this job last week to replace the CU's with one.

What is going on with this cut out and the neutrals. IMG_1736 - EletriciansForums.net

Another 'favour'. It's my last. After that I'm not doing any more. Everything possible went wrong.
Oh, by the way, I've always rated Wylex but the latest 'new type' are awful.
 

pc1966

Esteemed
Arms
Reaction score
11,027
It looks like it bypasses the meter - very dodgy - but equally it is not exactly hidden from the meter reader / smart meter installer.

Is it a really crap installation for communal lighting or similar that is not metered?

EDIT: Seen your drawing and the two from the cut out are N - but bypassing the meter - very odd, possibly a legacy of having other stuff in the past.

Really something that should be tidied up.
 

Reply to What is going on with this cut out and the neutrals. in the Electrical Forum area at ElectriciansForums.net

Similar Threads

Went back it a house after they upgraded shower to a 9.8kw, pulling 40a constant. We had wired it with 10sq and 40a RCBO. 10sq Neutral cable...
Replies
4
Views
505
Can anyone please shed some light on what this is/what is going on here? This old apartment is wired in conduit, which is also the earth...
Replies
5
Views
514
Hi the other day I opened the socket just to find out that 2 neutral wires were damaged with visible copper so I decided to cut them short and put...
Replies
11
Views
1K
I have an older Crouse Hinds board with a 200A service. Due to recent rehab on the house, I found I have the need to install a sub panel. I...
Replies
1
Views
436
  • Question
Hey there! I am fitting four lights in my kitchen and have come across two issues (pictures attached - this is really the best quality I could do...
Replies
4
Views
639
Advertise Here

New Posts (Please Reply)

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Top