I'm familiar with RCD spurs giving readings of 0.1 to 0.3MΩ when testing insulation resistance (L+N tied together to E), but what would give a reading of about 65Ω (when tested with "low resistance ohmmeter" i.e. continuity setting) N-E? On a lighting circuit - N isolated from other N's protected by the same RCD, and just for good measure the (double pole) RCD turned off (so if there's a borrowed N with another circuit, N on the circuit is still isolated from E at the PME block). RCD tests out fine, no reports of tripping.

I'll admit I didn't clamp L+N to see if there was actually any leakage... my working assumption is that this is an AC/DC thing - in the same way that if you measure the resistance across L and N when there's a transformer in the circuit (e.g. a shaver socket) it gives a very low reading, but it draws nothing at 50Hz.

I couldn't see any RCD spurs, but that doesn't mean there isn't one buried away somewhere... any I've never had a strange reading this low before.

What could it be?!?

Cheers :)
 
Is the rcd a true double pole? Disconnect the circuit and test again.

Could be any number of things, likely squashed or nicked cable somewhere.
 
  • Like
Reactions: happysteve
Hi - my quick thought is - if the DC reading was 65 Ohms but the AC impedance at 50Hz was much higher this implies an inductor (a choke).
 
  • Like
Reactions: happysteve
65 ohms is likely to be a fault where N and E are just barely in contact with one another. This might not trip the RCD if it's near the DB, especially on PME, because as radiohead points out there might never be enough voltage drop along the N conductor from DB to fault to drive 20+ mA through it.

I think the inductance idea may be a red herring. There's no reason for anything inductive to be connected between N & CPC, unless it's actually connected between L & N and the L is disconnected, etc, a bit far fetched.
 
Thanks all. Appreciate the responses. :)

In reply to some of the above:

- yep, definitely a double-pole RCD

- yep, aware of the usual causes of N-E shorts/low resistances

- thought about something inductive, but couldn't think of anything. As I said, I'm aware though of some items (like some BS7288 RCDs) that do give a low reading between the live conductors and the cpc, but usually in the 100's of kΩ, rather than 10's of Ω

- hadn't worked through the maths with respect to cable resistance vs fault resistance vs load current --> leakage current, I will have a think :)
 
  • Like
Reactions: radiohead
At 65 ohms you would need 1.95V between N & E at the origin to cause 30mA, so if the voltage is generally below 0.975V (which is likely in a TN-C-S setup) then you won't see enough earth current to cause a trip.

However, in many cases what you will see if it tripping unexpected when you have, say cooker on and shower in use, or vacuum cleaner started, and the peak demand goes to 60A or so then you would see that sort of voltage if there was a total of 16.25 mOhm resistance between the neutral bar in the CU and the combining point of the PME N+E.

That sort of resistance is rather high for that part of the installation, so unless you have very long tails (17m of 25mm, for example) and/or some dodgy contact resistance, it is not going to show up routinely.
 
  • Like
Reactions: happysteve
Found it (65Ω partial short N-E)... you're gonna love this... :) :

pull_switch.jpg


:tearsofjoy::tearsofjoy::tearsofjoy::tearsofjoy:

Given the white paint on the bare cpcs, my money is on the decorator.

Genius!
 
Found it (65Ω partial short N-E)... you're gonna love this... :) :

View attachment 59701

:tearsofjoy::tearsofjoy::tearsofjoy::tearsofjoy:

Given the white paint on the bare cpcs, my money is on the decorator.

Genius!
where's the Neutral? looks to me like a 2 way pull switch so what's the cpc doing in the swiych terminal?
 
where's the Neutral? looks to me like a 2 way pull switch so what's the cpc doing in the swiych terminal?
The neutral is the other side of the halogen lamp :)

explanation.jpg
 
  • Funny
  • Agree
Reactions: DPG and pc1966
I think they are single+CPC wires instead of the usual T&E

Just seen the diagram!
 
so it's actually a S/L to E Zero ohms fault, the 65 ohms being the cold resistance of the lamp.

obviously down to dodgy dave decorator man.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

happysteve

Broke Internet
Arms
~
Joined
Location
Nottingham
Website
http://www.dovecote-electrical.co.uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Dovecote Electrical

Thread Information

Title
What would give a low N-E resistance (at DC), but not cause the RCD to trip?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
happysteve,
Last reply from
telectrix,
Replies
11
Views
3,866

Advert