Please see attached electrical art. Please study and note my remarks beside the three balloons. The ohmmeter tests at A, B,C and D must be done with all sources of electrical energy ie mains, battery and pv panels isolated. With ohmmeter set to low range eg 0 to 200 measure between N and E/cpc and tell me results.
Hi Marconi
I think this will take me some time to do, as I will need to get access to the mains in my house and I am assuming the insides of the cabinet trunking and connections. To be honest it may be more than difficult to start dismantling the internal components of the cabinet as its all concealed, I will get in the cabinet and see what I can access and hopefully get back to you soon, I am working over the next three days on odd shifts so it may not be until the weekend or Monday.
I am assuming I is the inverter and the consumer unit on the right is my solar out unit.
Thanks for taking the time to do the drawing, I am very grateful.
My fears at present are that I am going to have to do some serious alterations to the set up and that was why I got a self contained cabinet to avoid this.
Quick edit I measured the point (b and c) before and after the rcd and got 00.2 for both and the consumer unit (D) with feed unplugged and all both on and off and got no reading. The main consumer unit is in a built in cupboard over the door and will take some getting to, so it may take me a while to get reading A.
We will see.
Regards
Tonyboy