ricardo123
Hi,
This is my first post and hope someone can help.
I have tested a TN-S system and have these readings, I am constantly getting a higher Zs than the Ze+R1+R2.
The Zs is about 0.01 to 0.04 higher than my Ze+R1+R2 readings.
My Ze is 0.14 and PFC 2.1KA.
I have zero'd all 3 leads seeing a resistance of about 0.15ohms.
I am doing a standard Ze test (I hope) disconnect main bonding to exclude any parallel paths, remove main earth from CU, main switch is off, using 3 test leads, one on earth the other two probes on the incoming live and neutral into the CU main switch. I am using a fluke 1652 set to L-PE, Ik on the Loop test setting.
Any help would be appreciated.
This is my first post and hope someone can help.
I have tested a TN-S system and have these readings, I am constantly getting a higher Zs than the Ze+R1+R2.
The Zs is about 0.01 to 0.04 higher than my Ze+R1+R2 readings.
My Ze is 0.14 and PFC 2.1KA.
I have zero'd all 3 leads seeing a resistance of about 0.15ohms.
I am doing a standard Ze test (I hope) disconnect main bonding to exclude any parallel paths, remove main earth from CU, main switch is off, using 3 test leads, one on earth the other two probes on the incoming live and neutral into the CU main switch. I am using a fluke 1652 set to L-PE, Ik on the Loop test setting.