Would you accept a Ze of 199Ω on a TT Installation which also has an RCD?

  • Yes

    Votes: 8 27.6%
  • No

    Votes: 21 72.4%

  • Total voters
    29

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,607
I realise many threads have been discussed around the (maximum) figure of 200Ω for external earth fault loop impedance (as given by BS7671) on a TT, however I'd be interested to see what proportion would and wouldn't accept this figure.

Hopefully we wont get into semantics of was it a dry day, wet day etc. Its just a straight forward simple poll seeing how many would accept the figure given by BS7671.

This will be an anonymous poll.

EDIT : I SHOULD HAVE SAID :

"WOULD YOU ACCEPT A Ze OF 199 Ω ON A tt INSTALLATION WHICH ALSO HAS RCD PROTECTION"
 
Last edited:
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

Should the option on the poll be below 200 ohms?

Yes.. bugger!

Can You change it mods?

I should have put 'Would you accept a Ze = 199Ω on a TT Installation which also has 30mA RCD protection'.

Hopefully you'll all see this and vote accordingly :smile5:
 
Last edited:
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

Does everything need to be a poll?

We'll be having designs put to a poll soon!
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

200 no


199 yes.

unless you are with the NICEIC and then its

100 no


99 yes

:rant::rant::rant:
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

Does everything need to be a poll?

We'll be having designs put to a poll soon!
Like any other thread, you have the option to ignore it if it doesn't interest you.

If it interests nobody it'll soon drop off the bottom of the page....
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

And I'd like to think that all TT systems will have an RCD, multiple RCD's in fact. Even if they meet TN readings I'd still be inclined to have an upfront Type S RCD...
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

Just don't show it to Tony Cable.
He will only frown at you for not listening to those who are above and beyond BS 7671.
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

Yes.. bugger!

Can You change it mods?

I should have put 'Would you accept Ze = 199Ω on a TT Installation which also has 30mA RCD protection'.

Hopefully you'll all see this and vote accordingly :smile5:

Do you mean Ra
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

let's put this stupid 200Ω myth to bed once and for all. it is NOT a max. figure in BS7671, which clearly states that a value above 200Ω is liable to be unstable. there is no mention of a max. figure in any BS7671.

for the record, i'd not accept it and i can't vote in the poll as there is a forum glitch. paul m is looking into it.
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

let's put this stupid 200Ω myth to bed once and for all. it is NOT a max. figure in BS7671, which clearly states that a value above 200Ω is liable to be unstable. there is no mention of a max. figure in any BS7671.

for the record, i'd not accept it and i can't vote in the poll as there is a forum glitch. paul m is looking into it.
Tel why is your text getting so small. (PS I've bought the bloody bonneville!!!!!)
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

I would want to see reading of less than 10, so keep swinging that hammer!!
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

Granted HHD , but you could have just as easily referred to it as Isc for that matter then ! After all terminology is quite important in our industry .
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

let's put this stupid 200Ω myth to bed once and for all. it is NOT a max. figure in BS7671, which clearly states that a value above 200Ω is liable to be unstable. there is no mention of a max. figure in any BS7671.

for the record, i'd not accept it and i can't vote in the poll as there is a forum glitch. paul m is looking into it.

Problem is its open to interpretation, to be fair it implies a 200 ohm ceiling, and that's where confusion can come into play.
Why state instability at 200 ohms if 100 ohms is going to be a cut off point.
They need to clarify and that's been the case for far to long, like I say jokers.

As a point of reference (for what its worth)
Table 45.1
Regulation 411.5.3
Note 2,
The resistance of the installation earth electrode should be as low as practicable.
A value exceeding 200 ohms may not be stable.
Refer to Regulation 542.2.2
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

Problem is its open to interpretation, to be fair it implies a 200 ohm ceiling, and that's where confusion can come into play.
Why state instability at 200 ohms if 100 ohms is going to be a cut off point.
They need to clarify and that's been the case for far to long, like I say jokers.

As a point of reference (for what its worth)
Table 45.1
Regulation 411.5.3
Note 2,
The resistance of the installation earth electrode should be as low as practicable.
A value exceeding 200 ohms may not be stable.
Refer to Regulation 542.2.2

You missed the actual table 41.5 (not 45.1), which says:
Maximum earth fault loop impedance (Zs) for non-delayed RCDs to BS... .... for U0 of 230V...

Rated residual operating current (mA)__________ 30 / 100 / 300 / 500
Maximum earth fault loop impedance Zs (ohms) 1667 / 500 / 167 / 100



So, an installation protected by a 30mA RCD with a circuit Zs of 1667 ohms would comply with the regs, providing that you could show that this was the maximum Zs under all conditions (and that it was not practicable to reduce it).

Not saying that this is 'right' or good practise.

My interpretation of the 200 ohm figure is that if a Zs of 200 ohms or less is measured, then the figure is unlikely to degrade enough to cause the required Zs value to be exceeded (with change of ground conditions). It's odd, however, that they don't give a lower 'may be unstable' figure for installations with higher rated RCDs. After all, even a rod with a low Ra will still vary, although by a lesser amount.
 
And, to answer the original question, for an installation protected by a 30mA RCD, I'd accept a Zs of 200 ohms on an EICR without any additional comment.

For a new rod, then I'd attempt to comply with the "as low as practicable" note (there's a subjective requirement if ever I saw one!).

Incidentally, I note that Ra includes the resistance of the earthing conductor and the final circuit cpc up to the exposed conductive parts.

In 411.5.3 the regs seem in some confusion between Ra, Zs and "the resistance of the earth electrode", which are, of course all different (although in most cases, not by much).

(Should be subscript 'A'; how do you do subscript?)
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

Granted HHD , but you could have just as easily referred to it as Isc for that matter then ! After all terminology is quite important in our industry .

You're quite right JD, I shall choose my letters more carefully next time.
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

You missed the actual table 41.5 (not 45.1), which says:
Maximum earth fault loop impedance (Zs) for non-delayed RCDs to BS... .... for U0 of 230V...

Rated residual operating current (mA)__________ 30 / 100 / 300 / 500
Maximum earth fault loop impedance Zs (ohms) 1667 / 500 / 167 / 100



So, an installation protected by a 30mA RCD with a circuit Zs of 1667 ohms would comply with the regs, providing that you could show that this was the maximum Zs under all conditions (and that it was not practicable to reduce it).

Not saying that this is 'right' or good practise.

My interpretation of the 200 ohm figure is that if a Zs of 200 ohms or less is measured, then the figure is unlikely to degrade enough to cause the required Zs value to be exceeded (with change of ground conditions). It's odd, however, that they don't give a lower 'may be unstable' figure for installations with higher rated RCDs. After all, even a rod with a low Ra will still vary, although by a lesser amount.

That's what happens when the old bugger doesn't put his glasses on.
Many thanks for correcting me kind sir.
Just wish they could come up with some decisive information or even come to a reliable conclusion as to what makes a max value stable and then at what point its not.
I have corrected TT system readings above 400 ohms.
And yet the 30ma rcd's protecting those circuits have, under test, operated within 40ms/200ms no problems.
If un-stability is a science it needs practical clarification so that we have a definitive cut off value that all adhere to with no grey areas.
In the mean time I will continue to go with 100 ohms purely because logic dictates its a safer bet than 200 ohms.
No other reason, and if someone proved conclusively that below 200 is still a safe option then so be it.
 
A meaningless poll without a 'depends' option.

I've accepted far higher, I've also refused to accept far lower.

Including the depends option, would be interested to know your reasoning behind acceptance vs refusal.
Its the one area where over the years I have never seen agreement on what determines a stable value.
At what point does one say yay or nay ?
 
How many electrodes and how deep do they go? A higher Ra value from multiple 8' rods properly spaced will be far more stable than a lower value on a single 4' long rod
 
Including the depends option, would be interested to know your reasoning behind acceptance vs refusal.
Its the one area where over the years I have never seen agreement on what determines a stable value.
At what point does one say yay or nay ?

That's the point there is no set stable value. The only way to determine stability is to test the TT system during different seasons of the year (eg wet and dry seasons) If there is a significant difference in Ra values between the two, then it's not stable. Generally you will achieve a good deal of stability from the depth the electrodes are driven, in decent soil conditions, and why i always advise a minimum of two extendable 5/8'' rods. You'll never in a month of Sunday's ever achieve a stable TT Ra value using a 1.2m thin twig.


You can however quite reasonably have a stable 200, 300, ....500 ohm electrode, which again makes the statement in BS7671 that many still use as a max Ra value, not worth the paper it's written on!!
 
The relevance was often a sore point back in the days when we were completing installations for petrol filling stations.
We worked at the time to the old HS G 41.
I believe BS/EN 60079 is the current standard alongside 3871.
We worked towards a value of sub 20 ohms for TT
Rod or earth plates being employed.
Often the general mass of steel work and even the tanks themselves would bring the values well down once main, and cross bonding were in place.
Now that's when the bonding regime of the 15th really came into its own.
The risks of diverted neutral currents left PME on the shelf.
Guaranteed TN-S was also used, but what was meant by guaranteed was any ones guess.
Always seemed a joke to see all the bonding, cross bonding, earthing arrangements, and precautions taken by the tanker drivers when hooking up.
And then along comes a young lad on his moped, straight into the hazardous zone, with a nice fat couple of thousand volt spark jumping across his dodgy HT lead.
 
DNO substations also work to a 20 ohm value, but very few will be anything like 20 ohm, most will indeed be sub 1 ohm, but then again, i've never seen 1.2 metre earth rods being used at any substation they would generally be 5/8'' or 3/4'' extendable 2.4 or 3.2 metre examples and will often be dropped into drilled bore holes surrounded by Bentonite or Marconite. Earth plates are fine the biggest drawbacks to their use is that the ground needs to be excavated first Which generally means that they are often not installed to any great depth, and you can't reliably test them until they have been backfilled and compacted. Same goes for copper tape grids, both systems being far more expensive to implement than installing ground rod electrodes...

Interconnecting different earthing systems say Ufer, underground metal tanks, and made electrodes also needs some thought put into it, as spheres of influence can overlap that can have detrimental effects to the overall Ra values, it's not just an easy case of connecting everything together and hoping for the best...

The bulk fuel tankers connect to storage tanks at filling stations and bulk storage facilities is a precautionary measure to reduce/eliminate any static electricity on the connecting pipework between carriers and static tanks that volatile fuel will be passing through.... I thought it was common practice NOT to fill vehicles at filling stations with the engine still running, i know it used to be....
 
...I've been in countless filling stations,where people are using their mobile devices,and engines are left running.

The most i have ever heard the staff say,is "Points card,sir?"....:conehead:
 
...I've been in countless filling stations,where people are using their mobile devices,and engines are left running.

The most i have ever heard the staff say,is "Points card,sir?"....:conehead:
don't really think it's an issue though, not heard of any petrol stations blowing up in the UK.
 
I was in Thame service station last year filling up and the tanker was there unloading at the same time . The next thing I know is the driver running across the forecourt after a skip waggon playing bloody hell !?

The skip waggon did not stop , and as the tanker driver was walking back past me he noticed that I was a little bemused , it turned out that the skip waggon driver had just filled up on a self service pump probably whilst still smoking because as he had reversed out to go off ( he had been in a car place and not a dedicated lorry one ) , he had flipped his tab out of the window at the feet of the tanker driver whilst he was still unloading !!!!
The old boy was still raging and said that it was a criminal offence and that he was going to get the video evidence and take it further .
 
don't really think it's an issue though, not heard of any petrol stations blowing up in the UK.

Nor i, it was always a precautionary rule that was generally adhered to in the day's when the petrol station attendants used to fill your car/bike etc at filling stations.... I imagine it's now ALL self service at filling stations in the UK... Not so in Cyprus, all are still attendant service from around 7am up until around 7-8pm then goes over to self service...

You need to see some of the filling stations i've seen in the Middle East and Asia, death traps just waiting to happen, you want to get in and out of there as quick as humanly possible!! And Yes i've seen a few of these establishments go up over the years, not at the time mind you, just seen the results of the aftermath!! lol!!
 
Think it's more of an issue at chemical plant off loading points with liquids such as vinyl acetate not diesel/petrol with different ignition points
 
Think it's more of an issue at chemical plant off loading points with liquids such as vinyl acetate not diesel/petrol with different ignition points

Nope, it's a very real issue at fuel storage depots, it'll be a tin tack job for a driver filling up a bulk storage carrier without first equalising his tanker to the depots equipotential zones pipework. I dare say the same would be the case at filling stations. Many people think that diesel tanks aren't that dangerous, but forget that highly volatile diesel fumes found at the top of all diesel tanks can be just as dangerous as petroleum as far as ignition points/values are concerned...
 
Nope, it's a very real issue at fuel storage depots, it'll be a tin tack job for a driver filling up a bulk storage carrier without first equalising his tanker to the depots equipotential zones pipework. I dare say the same would be the case at filling stations. Many people think that diesel tanks aren't that dangerous, but forget that highly volatile diesel fumes found at the top of all diesel tanks can be just as dangerous as petroleum as far as ignition points/values are concerned...
yes it's obviously an issue at storage depots, but i meant more the issue of phone use at filling stations compared to chemical plant off loading points.
at some off loading areas your not allowed to walk through with a battery powered pocket calculator!!
 
well in theory these do have the joule/watt energy to ignite some types of flammable vapours. And you don't want to be around when a 100M3 vessel goes up.This has happened in the past, a few been in the US, but there was one explosion in the north of England can't remember the sites name at the moment.
Flixborough in 74
 
Last edited by a moderator:
Another myth is the one surrounding risks relating to mobile phone use on a petrol forecourt.
I asked the question twice, once when a Gilbarco engineer was on his mobile, and the second was weights and measures.
Both were of the same opinion.
There is no evidence to support the use of a mobile poses any danger ??
Not saying they are right, but I have never found anything that would say they are wrong ???
 
Doesn't really matter if actually using the phone or not - if it's switched on in your pocket then it's still polling the nearest bases station and gauging signal strength/tx power etc. And like people have said above, how many explosions has it caused. In fact, I think it was Brainiacs or Mythbusters which tested this theory out by ringing a load of mobile phones in a gas filled caravan. Must have been Brainiacs thinking about it! Daz
 
As silly as it sounds it has been taken in to account. Many chemical plants and gas facilites do have a police presence, as is in the Grimsby area.

The east Yorkshire coast one near Holmpton/Withernsea has armed police patrols in the area. Can't remember the name of it. Daz
 
Nice area around there. Nice bit of military history at Kilnsea and Spurn point. Daz
 
Don't start giving these ISIS Jihad types any ideas for fooks sake!!!

Remember when working at a nuclear power station just after 911.
Security was tighter than the proverbial ducks bottom.
We needed to change a supply source during a re furb.
UPS system for comms was signed off as being healthy, and we were give permission to shut down, lock off and transfer.
We were there as a contractor, and the in house maintenance sparks were also present.
All good to go says the in house sparky's with a thumbs up.
No problem bud, says I.
As soon as you throw the switch we will start the transfer.
Oh !! right ok he says.
Ker clunk,
Should of had a full half hour, system went down in less than five minutes.
Now back then if comms go down, all hell breaks loose.
The UPS service engineers were for the high jump, and when they asked who had isolated the supply I was able to say "I know nothing senor"
Moral of the story.
Don't be the scape goat for somebody else's responsibility.:ack2:
 

Reply to Would you accept a Ze of 199Ω on a TT Installation which also has an RCD. in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
  • Article
Electrical2Go - Choosing the Right Cooling Fans - All You Need to Know We understand that choosing the right cooling fan can be overwhelming...
Replies
2
Views
126
The purpose of this thread is two-fold: to let you folks see an EICR from someone who's too lazy (or busy) to even bother forging his test...
Replies
15
Views
4K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
....TN-S appears outside, butt TT employed inside. Good Evening Everybody (This is my first post) Overview: The supply to my parent's cottage...
Replies
29
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock