V
VoltzElectrical
Please bear with me on this, as I have become totally confused and would like some clarification.
Scenario (hypothetical).
A 32 amp supply is required to supply a metal container 5m away from the main building. There is a spare way on the mains distribution board available. Is it permissible to use the supplier's earth (PME) either in the form of the cable sheath, or a separate core SWA for example, or is it a requirement that the container use only it's own earth in the form of a rod?
I.e. is it permissible to extend the equipotential zone of the building to include the container or not? I don't mean extend the PME, but use TNC-S from the board to the container and bonding too perhaps?
If anyone can advise on where I can find the answer that would be appreciated. I have been informed that the NICEIC don't like the supplier's earth used in this example, but I haven't dealt with them and have been led to believe from some posts on here that they like to make up their own rules?
Voltz.
Have a read of this: Wiring Matters - 2005 issues - IET Electrical
Issue 16 Autumn 2005 - Electrical Installations Outdoors: a supply to a detached building.
Voltz.
Wouldn't worry about the NICEIC mate, they don't write regulations, just refer to BS7671. If you require bonding or not may sway you as it would affect conductor size of your SWA for your 32A circuit e.g. 4/6mm and a Rod or 10mm if extending the PME.
Long time no see mate. You need to get back to posting more regular.
Thanks, it came up during a discussion the other day and I said I had recently connected one up. They asked 'how did you do it?' and I said the first way, i.e. by extending the equipotential zone. I was then told this was frowned on by the NIC who were the governing body.
Thanks Lee, been so busy this year, I have merely been an observer on here for so long, I genuinely had almost forgot my password :)
Remember the 10mm (if thats the size required for bonding) must be in addition to the earthing requirements for the submain and not inclusive of it so a seperate cable, additional core or larger cable may be needed to allow for it.
EDIT - As Davesparks has made me aware(Thanks :) ) I left out the vital info to this post.. I'm discussing using a SWA supply cable and the Steel wire cannot be used for bonding purposes therefore the above applies. It can be inclusive if a core or seperate but has to be additional if the steel is used as the circuit earth.
There is a scenario that can arise here when extending the equipotential zone - consider a metal container raised so insulated from the earth, you could see especially in a network fault a potential difference between the DNO earth and the true ground where the container sits... a dangerous situe for anyone that may create a path between the ground and container.. this may be why the NICEIC have reservations of it.. in such a case I would also drive a rod into the ground in addition to the extended equipotential bond.
Eh? A single conductor can satisfy both functions if it meets the required csa of whichever is the larger (usually the bond)
Reactions: 2 people
it's a metal container. that precludes the use of the PME in case there's a supply neutral fault. it's got to be made TT as you would for metal skinned caravans.
I can see the logic with that, maybe something BS7671 should address. Would you do the same if the container was not insulated from ground and was extraneous?
Nice pick up dave - I was refering to SWA where the armour cannot be used for the purposes of bonding so additional conductor is required or larger cable to ensure the earth core is big enough... I missed the key part of it out that its regarding swa Doh .. yep even I mess up :dozey:
Tbh I assumed you were referring to SWA sheath too, till Davesparks said that.
... I was refering to SWA where the armour cannot be used for the purposes of bonding so additional conductor is required or larger cable to ensure the earth core is big enough...
DW, can you please provide a reg that precludes the SWA acting as a bonding conductor?
It'll almost certainly never be possible in a TNCS supply, but if it's TT or TNS in a larger installation you may find the armour can comply as a bond.
If you have a normal building which is generally an insulated area then it is not too difficult to maintain a reasonable equipotential zone within the building, however for almost all areas using a TNCS supply it is very difficult to maintain the equipotential zone effectively outside of the building.
In the main this is not a major problem and the risks are low. Once you have a conductive material as the building then it is much more likely that in the case of a fault or a potential difference from system earth and true earth that you may have a shock risk as there is easy contact from the electrical system to the ground, this is why caravan sites and marinas try and avoid such situations and the DNOs do not like the idea of extending the equipotential zone beyond the walls of a building.
However then you want to look at the superior earthing system and better chance of fault protection from TNCS versus TT, balancing the risk factors would be site dependent, but in general I would go for the superior earthing system.
As Darkwood has said pinning the TNCS earth to the potential of true earth by the use of a rod can reduce the risk of shock when attempting to establish an external equipotential zone.
Only a possible issue if it is a PME supply, TN-C-S could be OK.
It's not as cut and dried as many seem to assume.
Ill give you the reason first then I need to look it up ... (PME systems)
The SWA as an earthing conductor is fine and is sized according to the requirements of the circuit thus in a fault it will trip the protective device in the required time, with PME set-ups the Bonding is sized in accordance to the possiblity of carrying N currents in a Network fault for long periods of time, the long term reliability of the SWA and its glanding was deemed not to be good enough for such a scenario especially with buried cables with infrequent testing.. I had this downloaded somewhere but that was on my old laptop that bit the dust, I now question whether it was a BS7671 requirement or the NICEIC stipulation on one of our jobs... I remember the DNO also got involved and requested a larger earth than our regs required due to network set-ups...
My problem is I use more than just the BS7671 and with the fact some of the sites I have been on have special requirements too I occasionally get a blurred lines between them all.. because I can see the scenario and the dangers I assume the BS7671 has them covered but seems they do fall short in areas.
earthing a container shed
VoltzElectrical,
telectrix,