At what size of SWA cable are you required to run an external earth ? I'm inspecting a distribution system and its a complete mess. No main earths anywhere but they have utilized the armour and are using at is their earth. I can't find anything in the regs book, is there possibly something in the guidance notes I can refer to ?
Hi Paul - if you've got GN8 its Appendix B. There's a few tables, this is just the first one. Hope that helps :)
SWA CPC.pdf
  • SWA CPC.pdf
If you are doing inspections you should know this being an electrical supervisor and all that.
There is no limit on size where a separate conductor is required, it depends on the individual conditions of the installation.
When assessing an existing installation the table 54.7 can be used as a first reference, but if this shows that the armour is inadequate you must then use the adiabatic equation as that may show that it is adequate.
Table 54.7 often gives a larger conductor size than is actually required.
You also need to consider whether the cpc also needs to perform the function of a bonding conductor, this usually changes things considerably.
Reply to SWA armouring as Earth in the UK Electrical Forum area at ElectriciansForums.net
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
5K
Hi, I have always used banjos when earthing the armour on an SWA but have now switched to earthing nuts. I am making off a 10mm fly lead to the...
Hi all I am after some advice on an installation I have coming up. Its a new TP+N circuit in SWA (13m run clipped direct) for a 22kW Tesla wall...