Ive recently been out to look at a kitchen refurb, where a split load mem memera 200 consumer unit is installed. The ring final circuit supplying the kitchen has 30mA RCD protection, no issues here. My issue is the oven supply. The OCPD is a 32a cartridge fuse which is on the non RCD side of the consumer unit.
The proposed work would involve the reposition of the old oven supply, utilising it for a new induction hob. This would involve chasing out into a wall and obviously the need for RCD protection. Im unsure due to the age of the board as to whether RCBO’s are available. With this in mind i suggested a seperate enclosure adjacent to the consumer unit to house a 63a DP RCD.
I would still be relying on the cartridge fuse for overcurrent protection in this setup, would it be better to install an RCBO in the enclosure? Just seems pointless to me.
Secondly does the enclosure need to be of metal construction? The consumer unit is of plastic construction and the suggestion of a new one to overcome the issues raised was pretty much flat refused.
Do you mean memera 2000?
If so the RCBOs are
come off the existing CU in 6.0mm from the fuse & N to a RCD in a plastic enclosure. then on to the cooker/oven. unless you can get a RCBO to fit in the CU,
Just noticed there, the rcbos on eBay are all sold as “used” so it’s a chance as to whether it works ok:confused:
A Memshield 2 will fit a Memera 2000 but not visa versa as the Memera 2000 has a narrower busbar tab. Strictly speaking they are not compatible due to the busbar size. True Memera 2000 rcbos were two module.
Personally i would get a small metal enclosure and bung a rcd in for the circuit you are working on. It does sometimes pay though to put a larger enclosure in so that in event of future works extra rcds/rcbos can be put in the empty enclosure for other circuits. prevents lots of 2 way boxes on the wall... as daft as it sounds larger enclosures are sometimes better priced than small ones???
I would be talking to the client about changing the CU - the board is obsolete and spares are pretty much all 2nd hand.
These conversations are difficult ........... but often a sensible course of action.
Totally agree and it was brought up, however i can only recommend.
Eaton do a compatible rcd field kit for Memera 2000 CU (Eaton MR30 rcd pod). They can be attached to a ALB 321 MCB.
It ain't cheap £100ish, and a big on the tall side. So if the wiring inside the CU is not tidy, you'll struggle to fit it.
That is an issue unfortunately as its a bit of a rats nest in the CU
Done it successfully a couple of times, last one however I was presented with same issue of untidy wiring.
Incidentally, I faced a similar predicament recently. I posted here and as well as the advice you've been given, others suggested placing hob mcb on RCD protected side of the CU. Which is what I did.
Unfortunately no spare ways in the RCD side of CU
Another issue on this job is that sockets are required for integrated appliances. I would normally position in an adjacent cupboard however i dont have that luxury with how the new kitchen is going to be installed. I have from left to right a fridge/freezer, washing machine and oven. The customer does not want FCU’s above worktop as that is the current setup and the worktops just look cluttered. Was maybe thinking off a bank of switches for all appliances but even then im unsure as to whether i have the space behind to fit a socket. Any other suggestions....??
Extend the flexes (within reason) of the appliances to a socket in next available floor unit or some might suggest flex outlets behind the appliances to your grid switches.
Reply to Seperate RCD enclosure in the UK Electrical Forum area at ElectriciansForums.net
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Deleted member 155212
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Hi, I've done some work in a house, I used an existing 10mm cable on a B40 MCB to supply a 2 way consumer unit to control a heat pump and...
I have a doorbell I want to install. The issue is the 16v transformer is designed to sit on a DIN rail. I have a 10 way 17th edition BG Nexus...
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...