Can the above method alone be classed as basic protection according to 131.2.1 it can. Based on that regulation you can leave live terminals exposed if supplied by a 30mA RCD
 
Isn't 'basic protection' where you can't touch any live parts by means of barriers, enclosures and things like that.
 
basically, it says that basic protection can be provided by making sure current can't pass through a body from direct contact with live parts, oe limiting that current to a safe level.

it does not say anywhere in BS7671 that you can have exposed live parts. the above reg. is meant for accidental contact with live parts if. for example, a cover is removed exposing those parts to touch.
 
I know it's not true but based on that reg alone it states :

Basic Protection
Persons and livestock shall be protected against dangers that may arise from contact with live parts of the installation.

This protection can be achieved by one of the following methods:

  1. Preventing a current passing through the body of any person or any livestock
  2. Limiting the current which can pass through a body to a non-hazardous valve
Now taking that to the letter without referring to any other regulation an RCD does exactly that, this is a very poorly written regulation and would afford you great defence in court.
 
but then 416.1 and subsequent regs, apply. you have no defence in court if you complied with 1 reg. and ignored another.
 
This protection CAN be achieved by one of the following methods:

It doesnt say "ohh and by the way not really" it clearly states you will have achieved basic protection
 
I know it's not true but based on that reg alone it states :

Basic Protection
Persons and livestock shall be protected against dangers that may arise from contact with live parts of the installation.

This protection can be achieved by one of the following methods:

  1. Preventing a current passing through the body of any person or any livestock
  2. Limiting the current which can pass through a body to a non-hazardous valve
Now taking that to the letter without referring to any other regulation an RCD does exactly that, this is a very poorly written regulation and would afford you great defence in court.
An RCD most certainly does NOT limit the current. It can't - the current is a product of Ohm's Law. It merely limits the duration if operating correctly.
 
agree. taking the human bod's resistance as 1K ohm, current is 240/1000 = 240mA. so a 30mA RCD will carry 8 x Idelta n. most RCDs trip at under 10mSec @ x5, so that limits the duration.
 
I know it's not true but based on that reg alone it states :

Basic Protection
Persons and livestock shall be protected against dangers that may arise from contact with live parts of the installation.

This protection can be achieved by one of the following methods:

  1. Preventing a current passing through the body of any person or Limiting the current which can pass through a body to a non-hazardoany livestock
  2. us valve
Now taking that to the letter without referring to any other regulation an RCD does exactly that, this is a very poorly written regulation and would afford you great defence in court.

I think you will find that limiting that current/duration,based on a 30mA rcd,will not provide any basic protection to certain members of our livestock community.....only another phone call to the knacker man.
 
Flawed argument we have either achieved basic protection or we havent, and if we haven't then the regulation 131.2.1 is nonsense
I have already pointed out why you haven't met the requirements of that Regulation with an RCD so how is it flawed?
 
Because by definition basic protection stops the flow of current and also by definition an RCD provides basic protection regulation 131.2.1 says it does,
Where does Regulation 131.2.1 state or even imply that an RCD provides basic protection?

Also I would suggest that basic protection prevents you from coming into contact with live parts as opposed to stopping the flow of current. (We used to refer to it as protection against direct contact.)
 
Don't get me wrong I totally understand the principle I'm simply pointing out the ambiguity of the regs
But I don't accept that it is in any way ambiguous. That's why I am asking where precisely you believe that the Regulation in question supports your claim.
 
The title of reg 131.2.1 is : Basic protection (protection against direct contact)
I know I'm simple, but I don't need to think much beyond that do I? :)
 
I know it's not true but based on that reg alone it states :

Basic Protection
Persons and livestock shall be protected against dangers that may arise from contact with live parts of the installation.

This protection can be achieved by one of the following methods:

  1. Preventing a current passing through the body of any person or any livestock
  2. Limiting the current which can pass through a body to a non-hazardous valve
Now taking that to the letter without referring to any other regulation an RCD does exactly that, this is a very poorly written regulation and would afford you great defence in court.

What would your rcd do if you decided to prod at line and neutral?
 
I know it's not true but based on that reg alone it states :

Basic Protection
Persons and livestock shall be protected against dangers that may arise from contact with live parts of the installation.

This protection can be achieved by one of the following methods:

  1. Preventing a current passing through the body of any person or any livestock
  2. Limiting the current which can pass through a body to a non-hazardous valve
Now taking that to the letter without referring to any other regulation an RCD does exactly that, this is a very poorly written regulation and would afford you great defence in court.

What would your rcd do if you decided to prod at line and neutral?
 
I know it's not true but based on that reg alone it states :

Basic Protection
Persons and livestock shall be protected against dangers that may arise from contact with live parts of the installation.

This protection can be achieved by one of the following methods:

  1. Preventing a current passing through the body of any person or any livestock
  2. Limiting the current which can pass through a body to a non-hazardous valve
Now taking that to the letter without referring to any other regulation an RCD does exactly that, this is a very poorly written regulation and would afford you great defence in court.

What would your rcd do if you decided to prod at line and neutral?
 
Why do we have a 30ma RCD if the result is a pass through of a massive current, it would make a mockery of it
It means that it will operate if there is a nominal 30mA earth fault current through it (between 0.5 and 1 times this in reality). So if you were in contact with a phase conductor and 30mA passed through your body it should operate. The 30mA rating has nothing to do with limiting the fault current to 30mA as this would defy Ohm's Law.
 
I see so what's the point of that level, 30mA
To protect human life.

It's not about limiting the current to 30mA but ensuring that it operates if 30mA is passing through - well actually 150mA for additional protection to operate within 40mS.
 
To protect human life.

It's not about limiting the current to 30mA but ensuring that it operates if 30mA is passing through - well actually 150mA for additional protection to operate within 40mS.
But if the result is an instant huge fault current that starts way above that figure why have it, hence my argument that the fault current grows from zero and fast.. In milliseconds; but is nipped in the bud by the RCD before it gets the chance. Plus if your argument is true why doesn't a 500mA protect you.
 
Last edited:
30mA RCDs are designed to trip when they detect earth leakage greater than 30mA.
Most will trip below this figure.
So if an RCD detects an earth fault current of 4600A, it will trip, and it will trip within 40ms.
An MCB will also trip if it detects a fault current of 4600A, though it is more likely to trip instantaneously or within 10ms.
Where RCDs are good, is that they will trip at lower currents which an MCB might not trip at, or may take seconds, minutes, hours or even days to trip.

So no, RCDs do not limit fault current, just as fuses and MCBs don’t limit fault current.
 
Explain the fault curve on a fuse chart if earth fault current doesn't grow with time. It shows how long it takes the fault to grow to a large enough magnitude to rupture the fuse. An RCD gets that curve chopped early. But by a means of imbalance measured via earth leakage
 
Last edited:
Well I would like to know the science behind how it saves your life if it doesn't limit the current your body receives
Imagine you’re outside mowing your lawn with your hover mower.
The grass is damp, the cable is damp, you accidentally cut through the cable.
You make the mistake of picking up the damp live part of the cable.
You get a belt, you fall down and are unable to release the cable.
Because there’s no CPC in the cable and you’re outside, the fault path is via the general mass of the earth, which in your garden has a high resistance. So high in fact, that there is not enough current to cause the MCB to trip.
You manage to hang on to life for 20 mins, unfortunately it takes your partner 30 mins to wonder what you’re doing and come looking for you.
If there had been a working RCD, the power would have been cut off in 40ms, you’d have got a belt and your arm might ache for the rest of the day.
 

Reply to Automatic disconnection of supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Cathodic Protection Station with Switching Power Supply for Buried Metal Structures Benefits of the Switchmode Cathodic Protection Rectifier...
Replies
1
Views
511
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
325
Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock