hi all,

Can anyone advise me regarding installing a triple pole mcb in a 3 phase board across phases. Simply put, if the next available ways in the board were for example 2L3,3L1,3L2 and placed my breaker here would this be acceptable?
This would normally be grey, brown, black. Hence 1 phase on 2 and 2 phases on 3. I know this will work however if the board were full and perhaps unbalanced, I would be splitting a load?
Would best practise be to use a single L1,2,3 for the breaker?

Hope this makes sense?
 
Im not sure if there’s any regulations prohibiting this but I feel it isn’t right and is bad practice. Would be far better to rearrange the mcbs to gain a correct 3phase position without having to go across different circuit numbers. Plus lableing the circuit would appear confusing....an isolator/accessory marked “3L123” is easier to follow than “2L3,3L1,3L2”
 
Im not sure if there’s any regulations prohibiting this but I feel it isn’t right and is bad practice. Would be far better to rearrange the mcbs to gain a correct 3phase position without having to go across different circuit numbers. Plus lableing the circuit would appear confusing....an isolator/accessory marked “3L123” is easier to follow than “2L3,3L1,3L2”

thank you, a sensible and reasonable answer! thought as much!
 
  • Like
Reactions: KEV 1 N
As stated it's poor practice. In fact other national standards (including ET101) specifically prohibit this practice.
 
As stated it's poor practice. In fact other national standards (including ET101) specifically prohibit this practice.

Thank you, now we've established that, can i ask, am I right regarding the fact that because you would breach 2 phases you wouldn't be able to balance correctly?
In a over the top example, if all L1 phases were in use and the board was full (other than this breaker) and you did this, you would be potentially overloading this phase? i hope this makes sense, cant think of a better way of explaining it.
 
When designing an installation (or addition or alteration) obviously you should try to balance the load across the phases as evenly as possible.
 
Thank you, now we've established that, can i ask, am I right regarding the fact that because you would breach 2 phases you wouldn't be able to balance correctly?.

You wouldn't be breaching two phases, it would still be connected to the same phases and the effect on the balance of the installation woukd be the same wherever you put the breaker.
 
  • Agree
Reactions: westward10
Hello Kris this is your original thread tidied up and now in the Trainee section. Your new thread which appears to be the same I have closed. Are you happy for it to stay like this?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

kris jones

Mentor
~
Joined
Location
shropshire

Thread Information

Title
3 phase breaker across 2 phases?
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
kris jones,
Last reply from
westward10,
Replies
7
Views
320

Advert