How can you guarantee that the person unplugging the equipment will be instructed?
How can you guarantee that the equipment will always be plugged back into the same socket-outlet?
What difference would it make whether the equipment is or isn’t plugged back into the same socket anyway?
Because it through the risk assessment is a controlled environment..
All equipment and associated sockets will be labeled as per regulations..
And as you say it won’t matter, as long as it is all designed and implemented correctly
 
Omitting RCD protection for stationary equipment that will only ever be unplugged for replacement or servicing by skilled/competent persons is one thing.
Omitting RCD protection for equipment that will routinely be unplugged for cleaning by ordinary persons is another.

I honestly think that if you were willing to sign a Risk Assessment stating RCD protection is not required in this instance, you would be considered incompetent or a fraudster in a court of law.

That is quite simply a ridiculous comment.
 
How can you guarantee that the person unplugging the equipment will be instructed?
How can you guarantee that the equipment will always be plugged back into the same socket-outlet?
What difference would it make whether the equipment is or isn’t plugged back into the same socket anyway?

Since when was unplugging something something that needed to be done by someone skilled?
 
Because it through the risk assessment is a controlled environment..
All equipment and associated sockets will be labeled as per regulations..
And as you say it won’t matter, as long as it is all designed and implemented correctly
The exception for skilled and instructed persons using socket-outlets has been removed.
Again the exception for specifically labelled or otherwise suitably identified socket-outlets has been removed.
Both of the exceptions were removed in 2015 amendment 3 of the 17th edition.

Producing a Risk Assessment that relies on outdated and non-compliant exceptions, would not to my mind be acceptable.

What I’m asking what difference does it make whether the equipment is plugged back into the same socket-outlet?
 
Since when was unplugging something something that needed to be done by someone skilled?
It never has done.
What has happened is the Regulations since 2008 have required RCD protection for socket-outlets used by anyone who is not skilled or instructed.

I’m not surprised at your lack of knowledge in regards to this matter, as it’s pretty consistent with previous posts you’ve made.
 
The exception for skilled and instructed persons using socket-outlets has been removed.
Again the exception for specifically labelled or otherwise suitably identified socket-outlets has been removed.
Both of the exceptions were removed in 2015 amendment 3 of the 17th edition.

Producing a Risk Assessment that relies on outdated and non-compliant exceptions, would not to my mind be acceptable.

What I’m asking what difference does it make whether the equipment is plugged back into the same socket-outlet?
Don’t forget this is not a domestic environment.. everyone involved in that environment will be competent in their own right and in those duties bestowed upon them..
The importance of plugging the stationary equipment back into their respective sockets is down to the fact that there is a discrepancy of + 16anps to 32 amps per phase when selecting between different sockets...
One socket may be fused at 20 amps whilst another may be fuses at 32amps so, why do you think it is important not to get them mixed up?
 
It never has done.
What has happened is the Regulations since 2008 have required RCD protection for socket-outlets used by anyone who is not skilled or instructed.

I’m not surprised at your lack of knowledge in regards to this matter, as it’s pretty consistent with previous posts you’ve made.

What a pity you intend on being rude.
 
Don’t forget this is not a domestic environment.. everyone involved in that environment will be competent in their own right and in those duties bestowed upon them..
The importance of plugging the stationary equipment back into their respective sockets is down to the fact that there is a discrepancy of + 16anps to 32 amps per phase when selecting between different sockets...
One socket may be fused at 20 amps whilst another may be fuses at 32amps so, why do you think it is important not to get them mixed up?
Doesn't matter that it’s not domestic.
The exceptions have been removed.

Ah, so now we know that the various sockets will not be fused according to the maximum rating of the sockets but to the various ratings of the individual items of equipment.

Again what difference would it make as to whether RCD protection is provided?
 
I’m not disputing the need for a plug and socket only the need for RCD protection..
Up until now equipment in this environment hasn’t needed to be considered for RCD protection..

Over the years there have been many things which have changed in the regulations resulting in this same type of situation. Something now needs to be done differently to how it used to be done, why not accept the change as a chance to improve safety rather than fighting against it?

People reacted the same way when RCDs became a requirement for all general purpose socket outlets regardless of whether they could be used outside or not, now everyone just accepts it as the norm. In a couple of years time the general consensus will change and this situation will be accepted as the norm.
 
The purpose of A Risk Assessment is to identify potential risks and hazards. Then put in place measures to minimise each of the risk’s.

In this case we would have to identifying if there is a risks of HAVING the RCD in circuit in order for there to be a risk reduction in omitting the RCD.
 
Why are people so dead set against having RCD protection fitted to these socket outlets?

There are very specific circumstances where the 30ma RCD can cause genuine problems. One i deal with regularly is sockets to supply temporary electrical distribution for entertainment ie sound and lighting for festivals. The overall earth leakage of the connected equipment can add up fast without being near 32amp load. These sockets generally connect to portable power distribution that has individual rcbo’s on each circuit. The original proposal to rase the requirements for rcd’s to 63amp where thankfully dropped.

But this is way off topic. Apologies.
 
There are very specific circumstances where the 30ma RCD can cause genuine problems. One i deal with regularly is sockets to supply temporary electrical distribution for entertainment ie sound and lighting for festivals. The overall earth leakage of the connected equipment can add up fast without being near 32amp load. These sockets generally connect to portable power distribution that has individual rcbo’s on each circuit. The original proposal to rase the requirements for rcd’s to 63amp where thankfully dropped.

But this is way off topic. Apologies.

I work in the same area, theatre and outdoor events. 30mA RCDs don't cause problems, the inappropriate use of them causes the problems.

I can't say I've ever had a problem providing 30mA RCD protection to final circuits.
Problems only happen when people do stupid things like putting distribution circuits on 30mA RCD.
 
I work in the same area, theatre and outdoor events. 30mA RCDs don't cause problems, the inappropriate use of them causes the problems.

I can't say I've ever had a problem providing 30mA RCD protection to final circuits.
Problems only happen when people do stupid things like putting distribution circuits on 30mA RCD.

Yes exactly. Im talking about the supply socket for the distribution to connect to.
 
Simple really. Either fit an RCD or the designer conducts a risk assessment, bearing in mind they will have to justify their decision that RCD protection was not necessary, possibly in a court of law, especially if someone was killed or injured as a result of the RCD protection being omitted.
 
Why are people so dead set against having RCD protection fitted to these socket outlets?

Not dead against. Just accepting that they are not always required and are not always necessary.

For example we install 32A TP+N sockets for retail kiosks on stations. We do not install these on RCDs as they will ultimately be distribution circuits so our risk assessment will insist that the kiosk will have all circuits independently protected by RCDs.
 
Not dead against. Just accepting that they are not always required and are not always necessary.

For example we install 32A TP+N sockets for retail kiosks on stations. We do not install these on RCDs as they will ultimately be distribution circuits so our risk assessment will insist that the kiosk will have all circuits independently protected by RCDs.
Are you telling us that you get such RAs accepted by National Rail and TFL?
 
I suggest you read back through the thread from the start!
I have only given constructive advice!
Please prove otherwise..
I have been involved in the installation and repair of commercial catering equipment for 25 years, I am an approved engineer for many brands.
What has been suggested is totally unnecessary..
just because you can’t do something doesn’t mean that it can’t be done, a risk assessment in this instance would be easy enough..
It’s stationary equipment that doesn’t need RCD protection
Are you sure about what you are saying here??
Are you uo to date with BS7671???
 
I suggest you read back through the thread from the start!
I have only given constructive advice!
Please prove otherwise..
I have been involved in the installation and repair of commercial catering equipment for 25 years, I am an approved engineer for many brands.
What has been suggested is totally unnecessary..
just because you can’t do something doesn’t mean that it can’t be done, a risk assessment in this instance would be easy enough..
It’s stationary equipment that doesn’t need RCD protection
Are you sure about what you are saying here??
Are you uo to date with BS7671???
 
I got bored with all the cat fighting and haven't read the entire thread, so forgive me if I've said something that has already been said.

If you decide RCD is the way to go, Hager do a range of three-phase RCD's. They are not cheap, but you can often find them on ebay.fr second hand. There is nothing wrong with them. They are usually from domestice installations in the rural areas which are often three-phase and some UK sparkies change them to single-phase so the RCD's are just surplus. Search for "Hager differentiel tetra"
 
Hi Norah
Thanks for the advice on reading the regs..
In a commercial kitchen where would you put a 3 phase RCD protected socket to protect a piece of stationary equipment; such as say a twin deep fat fryer or a 20 grid combi oven?
That little book you hold so dear hasn’t got all the answers, what will you do now?
 
Given the propensity of electric heating elements inside catering equipment to break down to earth I would want to fit RCD protection regardless. Better that (and an annoyed customer as the RCD starts tripping intermittently in the future!) than the black mess that will result from the circuit not disconnecting until the MCB pops.
 

Reply to 415v 3 phase sockets and rcd protection. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
774
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
879
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
863
What are people fitting in the 3 phase range just lately, I've had a scan at various makes and it seems to be a ---- up between Hager and Wylex at...
Replies
9
Views
883
Hi guys, I am rewiring a commercial launderette with 3 phase machinery. Does the machinery need to be RCD protected being in commando sockets...
Replies
5
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock