Discuss 415v 3 phase sockets and rcd protection. in the UK Electrical Forum area at ElectriciansForums.net
I got bored with all the cat fighting and haven't read the entire thread, so forgive me if I've said something that has already been said.
If you decide RCD is the way to go, Hager do a range of three-phase RCD's. They are not cheap, but you can often find them on ebay.fr second hand. There is nothing wrong with them. They are usually from domestice installations in the rural areas which are often three-phase and some UK sparkies change them to single-phase so the RCD's are just surplus. Search for "Hager differentiel tetra"
Hi Norah
Thanks for the advice on reading the regs..
In a commercial kitchen where would you put a 3 phase RCD protected socket to protect a piece of stationary equipment; such as say a twin deep fat fryer or a 20 grid combi oven?
That little book you hold so dear hasn’t got all the answers, what will you do now?
Given the propensity of electric heating elements inside catering equipment to break down to earth I would want to fit RCD protection regardless. Better that (and an annoyed customer as the RCD starts tripping intermittently in the future!) than the black mess that will result from the circuit not disconnecting until the MCB pops.
Reply to 415v 3 phase sockets and rcd protection. in the UK Electrical Forum area at ElectriciansForums.net
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
What are people fitting in the 3 phase range just lately, I've had a scan at various makes and it seems to be a ---- up between Hager and Wylex at...
Hi guys, I am rewiring a commercial launderette with 3 phase machinery. Does the machinery need to be RCD protected being in commando sockets...
4K