Hi All

I’m presuming a standard pendant is a class 2 fitting as the earth terminals are not needed as it’s a plastic fitting and it only has an insulated 2 core going to the actual ‘lamp part’.

Am I correct in thinking this?

The reason I ask is Screwfix have replied to someone’s question that it is a class 1 and requires an earth? Even though it is only used to loop in/out.

Can anyone clarify this for me.

Thanks E4F9170E-4F95-44C1-B671-7ACCE8B5BBFF.jpegA7B978CF-7918-4E13-8D37-39AFE2E772C6.jpeg
 
I'm more interested in who asked the question on Screwfix?
 
I would say the pendant as a whole is NOT class 2. It has an earth terminal and so cannot be defined as class 2.
 
  • Agree
Reactions: Jim_e_Jib
I'd say that the earth terminal within an insulated pendant base is purely there as either a parking or loop terminal depending on the wiring method and serves no other purpose with regard to the fitting. So in a situation where the lighting cable has no cpc and rewiring just isn't an option at that time then the pendant is a far safer and satisfactory alternative to a metal Class 1 fitting.
 
I'd say that the earth terminal within an insulated pendant base is purely there as either a parking or loop terminal depending on the wiring method and serves no other purpose with regard to the fitting. So in a situation where the lighting cable has no cpc and rewiring just isn't an option at that time then the pendant is a far safer and satisfactory alternative to a metal Class 1 fitting.

Agree. But it's not classified as class II.
 
For flip's sake, that's my post blown out of the water. Cheers!

But then, hold on - that's only the holder part. The assembly is not class 2.
Haha, who knows? Maybe you're right. I wouldn't have said it was class I anyway
 
For flip's sake, that's my post blown out of the water. Cheers!

But then, hold on - that's only the holder part. The assembly is not class 2.
just checked a BG pendant and it has no symbols or markings to help us.
and for the first time ever, i have actually read the enclosed instruction leaflet and it also has no useful information.
 
just checked a BG pendant and it has no symbols or markings to help us.

I'm sure any assembly that has an earth point or an earth cable entering it cannot be classified as a class 2 device. I would put a fiver on it. And I'm from Yorkshire.

And if that has no symbols on it then that confirms it isn't class 2.
 
From definitions:

Class II equipment. Equipment in which protection against electric shock does not rely on basic insulation only, but in which additional safety precautions such as supplementary insulation are provided, there being no provision for the connection of exposed metalwork of the equipment to a protective conductor, and no reliance upon precautions to be taken in the fixed wiring of the installation (see BS EN 6 1140).
 
  • Like
Reactions: DPG and nicebutdim
We need a copy of BS61140 to properly work this one out, which we're not going to get, so you're fiver's safe @DPG (for now)
 
I believe pendants, or more specifically the lamp holder is a special case when it comes to regs.
Access to live parts, where anyone can easily stick a finger in and touch the pins.
Although I think new lamp holders don’t power up unless a lamp is fitted.

As for class I or II… A pendant is made up of a ceiling rose, basically a junction box, a length of 2 core flex and a lamp holder.
The double insulated symbol must only be for the lamp holder part.
 
  • Like
Reactions: nicebutdim and DPG
The vast majority of BC lampholders don't have any additional safety features , I think Crabtree did/still do one.
 
  • Like
Reactions: nicebutdim
There is no way that pendant holder it Class II is has exposed live pins. The part no is K1170RPWHI and the only site which shows that symbol is Amazon none of the other sites do.
 
Last edited:
There is no way that pendant holder it Class II is has exposed live pins. The part no is K1170RPWHI and the only site which shows that symbol is Amazon none of the other sites do.
So Amazon is adding unauthorised 'Double insulated' labels to a product?
Sounds a bit like my dubious market trader relative and his roll of self adhesive 'CE' labels.
 
So Amazon is adding unauthorised 'Double insulated' labels to a product?
Sounds a bit like my dubious market trader relative and his roll of self adhesive 'CE' labels.
Who knows but it is odd this product on other sites does not show it and its position and everything about it is odd.
 
My GF mum house has no earth on the lighting circuits, pre 1966 build, has some metal light fittings, she is 90 years old and does not want the house rewiring.
I changed a faulty metal class1 fitting for a pendant (to her disapproval) , have advised to replace the other remaining fittings cant do no more.
 
  • Like
Reactions: Dave OCD
There is no way that pendant holder it Class II is has exposed live pins. The part no is K1170RPWHI and the only site which shows that symbol is Amazon none of the other sites do.
Not from Amazon, I bought this from Screwfix.
 
Part number would be K1186WHI

I'm guessing it must be the 'shockguard' version, which only makes connection when lamp is fitted.


Edit: That part number isn't one of their shockguard pendants.
 
Last edited by a moderator:
It looks a bit ad hoc I would query it with MK.
I don't think it is. My preferred pendant sets are MK, they've always been like this as long as I've been using them. I like the terminals in them.

Here's another lampholder, don't know what brand. I bought it a while back from an online shop for a table lamp repair.

otherone.JPG
 
  • Like
Reactions: nicebutdim
Very odd I would never deem them Class II.
 
  • Like
Reactions: nicebutdim
I don't think it is. My preferred pendant sets are MK, they've always been like this as long as I've been using them. I like the terminals in them.

Here's another lampholder, don't know what brand. I bought it a while back from an online shop for a table lamp repair.

View attachment 95611

It's definitely not - I edited that last post while you were typing.

Makes little sense to have a double insulated symbol when, at most, slight pressure gives acces to live parts.
 
  • Like
Reactions: westward10
Part number would be K1186WHI

I'm guessing it must be the 'shockguard' version, which only makes connection when lamp is fitted.


Edit: That part number isn't one of their shockguard pendants.
I just tested the MK pendant set, and got continuity between the live terminal in the ceiling rose and one of the pins, without pressing it in, so no special safety guards as far as I can tell
 
I just tested the MK pendant set, and got continuity between the live terminal in the ceiling rose and one of the pins, without pressing it in, so no special safety guards as far as I can tell

Maybe the class 2 status can be when the device is in normal use, ie. When fitted with a bulb?
 
  • Like
Reactions: Jim_e_Jib
But that wouldn't satisfy the requirements for Class II. I know in BS7671 these lamp holders are somewhat an exclusion for exposed live parts so maybe that plays a part but I don't see it.
 
Turning this around a bit: I don't believe class I equipment is allowed to have exposed live parts either, but there's loads of earthed metal lamps out there with either bayonet or screw lampholders, that are deemed to be class I.

I can only conclude that, as you say, the lampholder is excluded from the requirements
 
The reason i asked is that i have no earth on lighting circuits and i need an EICR.

have spoke to NAPIT and NECEIC and they are just as confused, one states it's ok and will pass EICR, the other states it will fail, class 2.

What pendant like fitting would work in this situation as they will all need replacing if they are indeed class 2.

Cheers
 
The reason i asked is that i have no earth on lighting circuits and i need an EICR.

have spoke to NAPIT and NECEIC and they are just as confused, one states it's ok and will pass EICR, the other states it will fail, class 2.

What pendant like fitting would work in this situation as they will all need replacing if they are indeed class 2.

Cheers
Standard plastic pendant sets such as these have no exposed conductive metal parts, so the lack of CPC (earth conductor) doesn't make them any less safe in their installed state.

Wiring regulations require a CPC to every point, even to plastic fittings such as these, in case they should be changed in the future to class I fittings. So even if you change all your lights and switches to plastic, it will still receive a code, as it is non compliant.

Whether your inspector codes it as C3 (improvement recommended, but satisfactory) or C2 (potentially dangerous, unsatisfactory) is up to his or her own judgement.
 
Standard plastic pendant sets such as these have no exposed conductive metal parts, so the lack of CPC (earth conductor) doesn't make them any less safe in their installed state.

Wiring regulations require a CPC to every point, even to plastic fittings such as these, in case they should be changed in the future to class I fittings. So even if you change all your lights and switches to plastic, it will still receive a code, as it is non compliant.

Whether your inspector codes it as C3 (improvement recommended, but satisfactory) or C2 (potentially dangerous, unsatisfactory) is up to his or her own judgement.

I will relay this info to each electrician and get their verdict on it.

Thanks
 
  • Like
Reactions: DPG
Just spoke to NICEIC electrician and he stated these are fine as Class 2.

‘BG pendants have no exposed metalic parts and internals are not live unless you put a bulb in so they will be fine.
C3 if fittings are class 2. C3 if not.
consumer unit will need warning notice to say not to install metal fittings on lighting’

These fittings and again question asked/replied.


559BE534-A715-47F9-B031-C5EE84C63479.jpeg42469775-ABD3-4655-8910-D118F6306E38.jpeg

Cheers
 
Just spoke to NICEIC electrician and he stated these are fine as Class 2.

‘BG pendants have no exposed metalic parts and internals are not live unless you put a bulb in so they will be fine.
C3 if fittings are class 2. C3 if not.
consumer unit will need warning notice to say not to install metal fittings on lighting’

These fittings and again question asked/replied.


View attachment 95621View attachment 95622

Cheers

Loving that user name 😀😃
 
As Pretty Mouth wrote in post 33, there is no definitive answer to this, and it will ultimately come down to the opinion of whoever is conducting the EICR. I would have no problem with a modern pendant set (with earth parking terminal) used on pre 1970 wiring without a cpc, but that doesn't mean others wouldn't.
 
Cheers guys, i have also been informed that the Class 2 type MK/BG pendants have spring loaded pin terminals and only connect/make contact with the lamp in place. Again this obviously does not stop someone actually pushing the pins in i presume....

I will get some when i get chance, check them and reply back as someone above has stated differently.
 
I was looking at the safety pendants the other day. Does anyone know where they are required? I think pendants are like toasters and would never get approval if it was just invented.
 
  • Like
Reactions: bilabonic
I was looking at the safety pendants the other day. Does anyone know where they are required? I think pendants are like toasters and would never get approval if it was just invented.

I think this thread explains their use and my primary use for using them as they are class 2 and require no CPC, saves a very expensive/difficult partial rewire.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Is a standard Pendant a Class 2 fitting?
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
66

Advert

Thread statistics

Created
bilabonic,
Last reply from
Risteard,
Replies
66
Views
9,970

Advert