Nonsense, try reading them.
I’m sure it says on page 1 that they’re not retrospective.
And if you search the forum for “not retrospective” you will find a good number of posts by different members all saying the same.
Reactions: pc1966 and DPG
BS7671 is not retrospective (from memory page 4 states that) , however we do code the the current edition of the regs as stated in GN3.
to answer the question you have to assess the risk ,if only pure resistive loads are on an AC rcd no code or maybe fyi only, i would code C3 if other loads are present that don’t affect the testing of the (RCD) Residual Current Device at time of test,C2 if it causes rcd blinding and it does not function correctly.
Reactions: loz2754 and pc1966
I hate the description of the Regulations "not being retrospective". No such comment is made within the Note from the HSE. What it actually states is that compliance with previous iterations of the Regulations may not necessarily imply that the installation is now unsafe or that it requires upgrading. As such, it also doesn't rule out that aspects of it might actually be unsafe or require upgrading.
Looking at a MEM A100HE RCD earlier today (of which I've fitted many dozens over the years), and was surprised to see it caries the type A (sine wave over half sine wave) markings.
How long have type A RCDs been around? I assumed it was a relatively new thing.
This was a newer grey one, but I've looked at an older yellow one, and still the same markings.
I came across an old wylex one not long ago, and was also surprised that it was an A, and not AC
Reactions: cliffed
Most of the old Memshield 2 pods are type A.
Reactions: loz2754
We found a old MK LN range RCBO which has a Type A trip and a BS 3871 trip curve
Reactions: loz2754
@Julie.
My thinking, the capacity of which is limited, is that potential for issue exists due to the way in which this protective device operates and the fact that one new appliance has the potential to change that operation.
I take the above points, but believe old wiring colours aren't a good comparison as they will have no impact on a householder who doesn't tinker with fixed wiring in their home. Replacement of an old or failed appliance doesn't generally require consultation. Given that a significant number of domestic EICRs are carried out for the sole reason of complying with rental legislation, I feel this adds another layer to the issue as no one can look around the property and assume risk on the basis of appliances present at time of inspection.
Similarly, the issue of premature collapse doesn't generally involve variables - risk exists or it does not and remedial work is quite simple.
Furthermore, most inspectors who carry out EICRs won't have any means of detecting DC leakage, much less any interest in attempting to do so.
What I have taken away from this discussion is that a number of opinions in favour of not coding type AC RCDs are based on customer reaction. While I understand that position, I don't consider customer sensibilities to be a factor of testing and inspecting. It's an interesting discussion about what, on the surface, appears to be a simple issue.
Had My Napit inspection last week and the assessor of the bat within 10 mins of meeting he asked me how I code Type AC RCD's which I replied Code 2 & I swap them out or replace circuit breakers with Type A RCBO's wit clients consent, which he replied Good answers as it is now a Code 2 on EICR's with Napit and in their latest edition of their codebreaking Handbook...Phew! as I thought he was going to try catch me out lol
Reactions: cliffed
Really there would be circumstances where you might code it C2, but C3 is recommended especially if electronic equipment was sparse.
It will soon be C2 for all new amendments soon & the installation of New DB’s, scrapping perfectly correct DB’s😎
As Type AC RCD's are still compliant and permitted in Reg (531.3.3) and without knowing the value of the DC component (if any) I will C3 it.
Codebreakers DIY Guide has a lot to answer for and is certainly aiding the confusion for non competent persons carrying out EICRs.
Amazing these Regs just keep on changing, I wonder to suit other’s, those making a Mint from all these requirements.
Obviously times change & regulations need to be updated, but you’ve got to read between the pages & see what’s required.
Experience & Know How more important now, especially in existing installations
It's not the regs changing it's how the severity is coded, napit seem to be different to electrical safety first,at the end of the day the inspector does the coding,though they should be able to justify why the code was assigned.