Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU, replacing this cable is practically impossible as there is no way of getting down without going through other flats. Looking for some advice of how others have gotten around this?
Do I fit a small board at the main incoming downstairs and protect the cable with a time delayed RCD?
 
Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU, replacing this cable is practically impossible as there is no way of getting down without going through other flats. Looking for some advice of how others have gotten around this?
Do I fit a small board at the main incoming downstairs and protect the cable with a time delayed RCD?

Will a time delayed RCD meet regs?

At the end of the day if you can't meet regs then the cable may need replacing.
 
What is currently protecting the cable?
 
  • Like
Reactions: timhoward
Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU, replacing this cable is practically impossible as there is no way of getting down without going through other flats. Looking for some advice of how others have gotten around this?
Do I fit a small board at the main incoming downstairs and protect the cable with a time delayed RCD?
Hi, being its top floor, could you not run SWA cable from downstairs drill out and run up externally into loft space and drop down to CU position.
The only problem suppose would be gaining permission from the L/Lord to run a cable up the building worth making inquires or even running internally up landing stair case if possible.
 
What is the earthing arrangement for this flat @JJONESY4 ?
 
Hi, being its top floor, could you not run SWA cable from downstairs drill out and run up externally into loft space and drop down to CU position.
The only problem suppose would be gaining permission from the L/Lord to run a cable up the building worth making inquires or even running internally up landing stair case if possible.
Hi, thanks for reply problem is it’s in central London so there’s no chance of running a cable directly through the landings or exterior as they won’t alow it.
 
So what is the problem?
 
So what is the problem?
The distribution circuit is not compliant t&e not protected IMO this should be a departure. If that the supply cable shouldn't stop anyone rewiring the flat.
 
Isn't protected by what, a 30ma RCD?
Not going to be part of the job if you are rewiring the flat.
 
sub main looks like it will need Rcd protection, the other issue is the size of the cpc which will be ok if MBPC are not required at the Flat.
 
The only reason it may need rcd protection is if it’s buried <50mm inside the other flats, and we don’t have that information.

It’s no different than regular meter tails in terms of mechanical protection… it’s just a long length, which is taken care of by the 60A fuse.
 
OP - is this T&E run on the surface or in conduit all the way? Or is any of it below the surface?

I'm guessing not as you were talking about changing the cable or adding RCD protection.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Kent
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Mains cable to consumer unit top floor flat
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
18

Advert

Thread statistics

Created
JJONESY4,
Last reply from
DPG,
Replies
18
Views
2,549

Advert