Discuss Zs a little out, what can I do to fix it? in the UK Electrical Forum area at ElectriciansForums.net
I
Inteificio
Hi.
Am working in a factory, most of the machinery on the main floor is fed from are fed from spurs (2/3 machines per spur).
As they have all been fitted with D type breakers, we need a tight Zs.
We have not got it.
I am trying to think of the easiest way of fixing it.
Turns out I'm not 100% sure what you can do with CPCs.
If each circuit has it's own dedicated CPC, can I also link a supplementary CPC (or even make a link between each CPC to have a star supplementary earth in addition to the original?)
I've flicked through the regs and can't find any info on supplementary earths!
The way I read it, is as long as all the CPCs are in the same enclosure you can do what you want!
Anyone with a bit more experience got a few tips?
Thanks,
Sorry for not giving more details.
Existing circuit that seems to be thrown together from spare parts.
Break size from 20 up to 32.
Zdb a rather nice 0.09
I have done most investigation on 1 circuit as I got a shock off it (from touching the chassis!!!)
D20 Zs 1.18
All circuits are feeding a selection of 3phase 16/32, single phase 16/13. Equipment is moved around room a lot so load varies.
Basically it is a mess, hence why I need help!
To solve your problem in the most efficient and best way, you should contact an expert to do it. They will check it up and could fix the damage as well. If you will do it by yourself, then there is a big possibility that you get to risk.
if the trunking is steel, then use that as well as a parallel path.
I would run supplementary bonding to any nearby steelwork, and also common the CPCs to the machinery, by Bonding them all to Common steelwork. It's in our contract specifications to do this, but I think it's good practice, and doesn't take long. Even linking nearby containment together can reduce Zs.
on our jobs we have to link any glands to the containment that feeds it, and also the chassis of any equipment, to maintain an equipotential zone.
Reason for shock is there was a disconnected earth. Only 24v on the chassis, not enough to cause harm, but enough to think WTF!
You must have soft hands...! I'd love to be able to feel a 24v shock!
I used to disconnect 8inch x 8 stack 50v live bus bars bare handed. I'm such a man ;)
RCD would be a simple solution, but we have a VERY limited budget at the moment.
The wiring is in plastic trunking on a floating ceiling, so not much to bond up there with a good connection.
I'm thinking linking all those earths is the cheapest, easiest solution.
I will see how that goes then, if problems, work out what to do next.
Thanks for the useful input ;-)
Like using larger CPC's from the DB!! ...lol!!!
We are very limited on space, and that would be 1 hell of a job. Linking the CPCs will have a far greater effect for less time and materials.
The last thing I want to do is be dragging in huge amounts of wire down 20mm copex.
Hopefully yes!!, but my reply was based on your comment....
In other words, if it doesn't provide the necessary results!! lol!!
Reply to Zs a little out, what can I do to fix it? in the UK Electrical Forum area at ElectriciansForums.net
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
So a quick catch up so you can get an idea… I was asked to do a job for another electrician, as he is too busy. I’m busy myself but said I’d...
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...