Discuss Rear entry three phase board in the Commercial Electrical Advice area at ElectriciansForums.net

Yes I don't see why not. Those red, yellow, blue and black conductors at the meter don't appear to be suitably enclosed.
 
Personally I am usually highly resistant to having concealed cable in commercial/industrial situations as I feel it must be accessible for inspection and testing. I also wonder how you will gland the SWA you are using? As you may know at least one end of the SWA must be earthed/terminated and connected with a fly lead to earth? How do you intend to seal the gaping hole?
The SWA is terminated to a metal box just behind the wooden board and the armour is earthed
 
Why did the rear entry hole have to be butchered so big and would it not made sense to consider a fire rated material as a backing board/entry grommet such as Paxolin?
There is no issue with the wooden board and there is no issue with a rear entry tho. It all conforms to BS7671
 
I can cut a hole in the wood boad maybe. Thank you I will make it accessible

I still don't think thats acceptable unless you make it big enough to be able to use spanners to check the tightness of the SWA gland

I would have run the SWA up to the bottom of the CU and glanded it directly to it - less parts, accessible .
 
Last edited by a moderator:
There is no issue with the wooden board and there is no issue with a rear entry tho. It all conforms to BS7671

I didn't question the rear entry, just the large size of it and the combustible material it's sat on. Potential fire containment is surely a consideration when choosing installation methods regardless of whether it's acceptable in BS7671?
 
To be constructive, a much better solution would be to

A) use the 3phase meter kit that Wylex make for this board that fits neatly inside utilizing the front bottom left knockout for the screen.

B) gland that armoured straight into the bottom.

C) If you wish cables to enter the rear a id drill a few 50mm holes rather than 1 huge one as sealing up is going to be untidy, you dont want a mouse in there!, i recently fitted one of these boards and went for rear entry for the swa incomer, but i could walk down an access behind the board so glanded in the rear properly
 
I would have brought the cables into a bit of 100x100 trunking below the DB, removed the plate at the bottom of the board and taken the cables up through a slot in the top of the trunking protected by a bit of paxolin or even rubber edging, maybe even grommet strip :eek:
I'd have glanded the SWA into the bottom of the trunking.
 
https://www.NoLinkingToThis/p/wylex...gclsrc=aw.ds&dclid=CKO3xb2Cjt0CFWwW0wodkFMJIw

Buy that.... Gland your swa in the top of the board properly, jobs a gooden...

Have you factored in the ccc for those tails in the trunking?
 
Last edited by a moderator:
https://www.NoLinkingToThis/p/wylex...gclsrc=aw.ds&dclid=CKO3xb2Cjt0CFWwW0wodkFMJIw

Buy that.... Gland your swa in the top of the board properly, jobs a gooden...

Have you factored in the ccc for those tails in the trunking?

I did suggest that kit to the customer before I started. He said he wanted to use the meter he already had.

What does CCC stand for, I do not know what the abbreviations you lot use. Is it Cable Capacity Chart?
 
Should have taken a step back and thought what is the best way to do this.
 
Last edited by a moderator:
The supply company feeds a meter, then it goes to the 1st board which feeds 4 sub boards, there is a meter before each sub board. The 4 sub boards are protected by 63A 3 pole CB's.
 
Last edited by a moderator:
?
The supply company feeds a meter, then it goes to the 1st board which feeds 4 sub boards, there is a meter before each sub board. The 4 sub boards are protected by 63A 3 pole CB's I said RCBO by mistake.
Usually, you would have an MCCB board with meters in the outgoing all in the landlord's cupboard.
 
Are all the outgoing circuit RCBO protected?
All the circuits from the board i installed will be RCBO protected
I would of done as Adam posted with the incoming SWA if you have to have that meter at that position would have been a trunking down the RHS SWA made off at top end cap then T off like you have done for the meter.
 
Are all the outgoing circuit RCBO protected?

I would of done as Adam posted with the incoming SWA if you have to have that meter at that position would have been a trunking down the RHS SWA made off at top end cap then T off like you have done for the meter.
You would have made off the SWA to the end cap of the trunking?
 
How would a MCCB prevent such an event?
If there is a fault on one of the final circuits you would want the MCB to trip faster than the MCCB. A practical example of this I recall was one of the final circuits we installed the chippy put a nail through the cable now as we had a low ELI it took out the RCBO as well as the existing 50A MCB protecting this D.B. bad discrimination ( sorry selectivity new word)
 

Reply to Rear entry three phase board in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi guys, So, a friend of mine has a three phase 100a supply and wants to install 2 x three phase 20a fork lift chargers and a three phase car...
Replies
24
Views
3K
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
887
Does a SPD need a dedicated way? I need an extra way in this unit for a 3 phase car charger As you can see its a small unit with no extra...
Replies
45
Views
2K
Hi everyone, this ones a first for me but weve been asked install and use a three phase supply in a large new build house. The 16 way dis board is...
Replies
5
Views
2K
Hello, I'm new to this forum, we are in the process of converting into 12 flats all electric, no gas incl. heating, showers etc. An electrician...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock