Bit big,the cutout,regarding IPXX etc
I am not sure wood boarding provides suitable containment in accordance with BS7671.does the wooden board not provide mechanical protection?
Will either use expanding fire proof foam foam or intumescent liningBit big,the cutout,regarding IPXX etc
The SWA is terminated to a metal box just behind the wooden board and the armour is earthedPersonally I am usually highly resistant to having concealed cable in commercial/industrial situations as I feel it must be accessible for inspection and testing. I also wonder how you will gland the SWA you are using? As you may know at least one end of the SWA must be earthed/terminated and connected with a fly lead to earth? How do you intend to seal the gaping hole?
It does there are many threads confirming thatI am not sure wood boarding provides suitable containment in accordance with BS7671.
The SWA is terminated to a metal box just behind the wooden board and the armour is earthed
I can cut a hole in the wood boad maybe. Thank you I will make it accessibleSo its inaccessible ................ not ideal
There is no issue with the wooden board and there is no issue with a rear entry tho. It all conforms to BS7671Why did the rear entry hole have to be butchered so big and would it not made sense to consider a fire rated material as a backing board/entry grommet such as Paxolin?
There is noting to bond in this building. No gas and plastic water pipes.If you look closely Mate you can see the screw holes fro a plate of some sort. A there doesn't seem to be any bonding conductors.
There will be no exposed cable what so everAs far as I am concerned you have opted for a poor installation method and they are not suitably enclosed.
I can cut a hole in the wood boad maybe. Thank you I will make it accessible
That is not the issue, you have single insulated conductors exposed to a combustible surface.There will be no exposed cable what so ever
There is no issue with the wooden board and there is no issue with a rear entry tho. It all conforms to BS7671
Hi,
Is it OK to create a rear entry in an eight way three phase BD.
Please see photo attached.
A technician friend of mine says he has never seen this done before?
View attachment 43904
Is it a plastic DB or metal one?I wouldn’t really worry about the back board being flammable, it’s probably less so than the plastic DB.
Why could the meter not be at the supply end?
https://www.NoLinkingToThis/p/wylex...gclsrc=aw.ds&dclid=CKO3xb2Cjt0CFWwW0wodkFMJIw
Buy that.... Gland your swa in the top of the board properly, jobs a gooden...
Have you factored in the ccc for those tails in the trunking?
Usually, you would have an MCCB board with meters in the outgoing all in the landlord's cupboard.?
The supply company feeds a meter, then it goes to the 1st board which feeds 4 sub boards, there is a meter before each sub board. The 4 sub boards are protected by 63A 3 pole CB's I said RCBO by mistake.
I didn't design that installation. Thank you for the heads up thoUsually, you would have an MCCB board with meters in the outgoing all in the landlord's cupboard.
Are all the outgoing circuit RCBO protected?
I would of done as Adam posted with the incoming SWA if you have to have that meter at that position would have been a trunking down the RHS SWA made off at top end cap then T off like you have done for the meter.All the circuits from the board i installed will be RCBO protected
An MCCB is not needed as the design current is not greater than 63A per phase.Usually, you would have an MCCB board with meters in the outgoing all in the landlord's cupboard.
You would have made off the SWA to the end cap of the trunking?Are all the outgoing circuit RCBO protected?
I would of done as Adam posted with the incoming SWA if you have to have that meter at that position would have been a trunking down the RHS SWA made off at top end cap then T off like you have done for the meter.
If there is a fault on one of the final circuits you would want the MCB to trip faster than the MCCB. A practical example of this I recall was one of the final circuits we installed the chippy put a nail through the cable now as we had a low ELI it took out the RCBO as well as the existing 50A MCB protecting this D.B. bad discrimination ( sorry selectivity new word)How would a MCCB prevent such an event?