Did you break the circuit up into sections to eliminate the faulty light fitting or just do a continuity test from light switch. How many light fittings are on circuit what is the overall load. Is it a new circuit
 
give up pete. it's like pulling teeth. maybe next week we'll get all the info. to give an educated guess.

You're right, 1st day back at work and I'm sick to death of answering daft questions, is it nice to be back Pete? wtf do you think?
 
RCD trips when light switch is turned on. Disconnected light switch and all loads and tested between l and n.
 
you need to IR test between L ans E and N and E. also there'a a possibility of a shared N if L and N are taken from different circuits.
 
  • Like
Reactions: 1 person
The RCD is tripping because of a fault to earth, that fact that it is delayed is either that the fault is near the limit of the tripping current or that the lights warm up a bit and let the water reach the expanded section.
The lights and all junctions need to be dry to prevent this sort of fault.
 
It's not a shared n. Been working for the past year they said. IR test 0mohms between L and N.

Could damp cause it to trip after 10 secs? Why dies it happen after that long. Surly with a short it would trip straight away?
 
The box seems to be damp.

That was my first hunch. Try and dry it out and see how you get on with ir tests
 
It's not a shared n. Been working for the past year they said. IR test 0mohms between L and N.

Could damp cause it to trip after 10 secs? Why dies it happen after that long. Surly with a short it would trip straight away?
A low IR test with a megger tester doesn't indicate a 'short' it indicates an insulation or earth leakage fault. Just incidentally if it's an RCD tripping fault why are you testing between the L+N instead of linking the L+N together and testing to earth?
 
  • Like
Reactions: 1 person
If we can get down to the nitty gritty of what tests you have conducted and how....it may shed some light (good pun) on whats causing the fault
 
Jiga, for hell's sake there's a procedure for fault finding. It's fairly basic stuff.
Put together a list of what tests you have carried out and how you have broken the circuit down and then maybe we can help you out.
 
  • Like
Reactions: 4 people
0m ohm is a dead short.
If you mean 0.0 MΩ then this could be any value of resistance up to 99,999Ω, or 49,999Ω if the meter rounds up.
Hardly a dead short.

Admittedly 0.0 milliohms (0 mΩ) is a dead short
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
10 second trip
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
48

Thread Tags

Advert

Thread statistics

Created
james king,
Last reply from
dingledong,
Replies
48
Views
3,664

Advert