Did you break the circuit up into sections to eliminate the faulty light fitting or just do a continuity test from light switch. How many light fittings are on circuit what is the overall load. Is it a new circuit
give up pete. it's like pulling teeth. maybe next week we'll get all the info. to give an educated guess.
Me today over my toolbox head butted the customers foot and got a nice carpet burn on my face
The box seems to be damp.
Have you ever had that feeling that I really need to be sectioned in the general publics interest?
A low IR test with a megger tester doesn't indicate a 'short' it indicates an insulation or earth leakage fault. Just incidentally if it's an RCD tripping fault why are you testing between the L+N instead of linking the L+N together and testing to earth?It's not a shared n. Been working for the past year they said. IR test 0mohms between L and N.
Could damp cause it to trip after 10 secs? Why dies it happen after that long. Surly with a short it would trip straight away?
IR test 0mohms between L and N.
Is it 0 ohms or 0mohms (milli ohms) is it 0Mohms (Mega ohms) whilst testing with a megger tester? You're confusing the kak out of me.0m ohm is a dead short.
Every day archy ! ! Oh you meant me !
I didnt do it on bloody purpose . It fookin hurt .I'm gonna take me Zimmer frame to work now
If you mean 0.0 MΩ then this could be any value of resistance up to 99,999Ω, or 49,999Ω if the meter rounds up.0m ohm is a dead short.
0m ohm is a dead short.