I know there’s the adiabatic equation to work earth size but generally if you install a twin and earth cable for distribution, do you need to worry about the smaller cpc size
My situation is 20 metre 10mm t and e run and not using it to provide earth bonding. Will the 4mm cpc be adequate. 50A mcb not many circuits to feed.
What's the Ze at source of circuit?
Type/rating of OCPD etc?
Installation method?
Reply to 10mm t&e submain cpc in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Apologies if this is in the wrong section - appreciate it's more of an educational question. That said I have 2391 - but the classroom environment...