If you are taking about bonding the gate or fence surrounding the TX, then UKPN stipulate 70mm2.
You need to look at the earthing configuration between HV and LV. If they are combined at the TX, the surrounding coupled earth electrodes need to be below 1 ohm (before cables are connected) to limit the touch voltage being imported into the LV installation, in the event of a HV fault.