Afternoon all,
Just wondering what everyone's response to the following scenario is.
Letting agents have asked us to carry out an EICR. There was a previous failed EICR that has been lost and isn't able to be retrieved. We were told that the landlord had had their own electrician in to carry out the required remedial works, but that they are no longer in contact and cannot get the certificate (I know, huge red flag). We have a very good working relationship with the agents so agreed, reluctantly, that we would carry out the EICR.
Naturally there were a few problems, but the biggest one is that it appears that a new consumer unit has been fitted. It's a fully metal Amendment 3 compliant enclosure so has to be no older than 2018, but they have fitted a single RCD main switch, no surge protection etc. Obviously we aren't fully aware of what has happened before, and under normal circumstances a single RCD on a residential EICR might only raise a C3. However, on the basis that the CU must be no older than 4-5 years, this should at the very least have a split load board. Therefore I'm giving the installation a C2 on this basis.
Anyone come across similar and handled it differently?
Afternoon all,
But you can't decide the code based on the age of the CU / when it was installed.
What is the regulation you are using to give a C2?
The rationale has to be about safety, not compliance with regs at a given moment in time.
Otherwise we wouldn't be able to code things like VOELCB's that were fitted before 1986, or class 1 light fittings without a CPC that were fitted before 1966. Both were compliant at the time but we now realise they are not safe.
I agree there are regs about avoiding nuisance tripping, but do you consider having an RCD main switch to be "potentially dangerous"? Or would you merely recommend this is improved?
I agree there are regs about surge protection, but there have always been circumstances where it needn't be fitted, and there still are, and again is it potentially dangerous? Or would you recommend this is improved?
We are told to inspect against the current regs but I'd be surprised if either of them constituted a potentially dangerous situation and they'd likely be a C3 from me.
@timhoward
This is a fair point with regard to C2 and whether you could argue potentially dangerous or not, but this is a single RCD board that has been installed recently with no certification given. Surely if the installation was never compliant to the edition of the regs under which it was fitted, it can't be deemed satisfactory?
@timhoward
The date that it was installed and the availability (or not) of a previous cert don't really affect the choice of coding though.
And there isn't really an argument that this is dangerous or potentially dangerous is there?
So there's no comeback then for the person who has changed the consumer unit in the first place, or the landlord that has gone with the cheapest quote from someone who can't/won't certify their own work? That consumer unit should never have been installed, but now that it has, it's 'satisfactory'. That doesn't sit right with me and opens up a can of worms in that any landlord could do any old thing, and as long as it doesn't raise anything worse than a C3 will get a satisfactory certificate, even when we know the installation wasn't carried out to the correct regulations?
Whether the customer wants to make any complaints to the previous installer is up to them. It has no bearing on any future EICR that is carried out.
I agree though, it sounds like a substandard install.
@timhoward
A lot of the time we have no idea if something was certified and it's a rare luxury to have access to any previous records.
The way I look at it is that we 'measure' the installation against the current regs.
But my opinion supersedes whatever the regs say about levels of danger and it's my opinion that counts!
Best Practise Guide 4 is quite clear that it's the level of danger that determines whether it is satisfactory or not. (Otherwise it wouldn't and couldn't recommend solutions to issues that are actually completely non-compliant)
In some circumstances even a Wylex Rewireable board could be deemed satisfactory.
You have to separate preference, justice, and EICRs!
If your customer quoted BPG 4 back at you it would get difficult to justify coding those as C2.
If it helps, imagine the EICR is for a prospective purchaser. And remember that EICR's shouldn't have different results depending on circumstances.
Ironically if this was a Wylex rewireable with an upfront RCD I'd probably give it a C3! (Depending on all the other factors involved, of course)
Food for thought here. I haven't sent the EICR to the agents yet and might mull it over on the weekend. I feel slightly aggrieved that I'll essentially be carrying the can, and likely doing the testing for someone else's rubbish board change.
Out of interest, if it weren't an EICR, and you went to a job where someone had had a recent board change but had fitted a single rcd CU, or a plastic CU, or something else that wouldn't raise a C2 but still clearly shouldn't have been done under the current regs, how would you handle it?
Depends what the job was. But it should be treated as per any other job. You can recommend the customer makes a complaint, but that's up to them.
Bin the job .Life is too short , weather is good !
everything that's been has past, The answers in the looking glass. There's four and twenty million doors On life's endless corridor,
the fact someone 6 days , 6 weeks or 6 months ago installed a rubbish consumer unit is neither here or there now
just do the EICR , code as you see it and tell the letting agent that the consumer unit is rubbish and offer to chance it for a bag
The satisfactory or unsatisfactory is in “terms of electrical safety, so I too would code it a C3.
Nuisance tripping is a different matter.
explain the best you can why you wouldn’t do it like that.
Everyday we price for all RCBO boards when a dual rcd is permissible. It’s the same explaination.
Who on earth is still fitting dual RCD boards
Batman Facepalm GIF by WE tv
Age of the installation does not change the coding on an EICR.
You are reporting on the suitability and safety of the installation for continued use, you are not reporting on absolute compliance with BS7671.
This is why an EICR is not permitted as a substitute for an installation certificate.
A single RCD on the whole installation is something which can be improved upon but is not potentially dangerous in any electrical sense so it is only a recommendation for improvement.
Then you should be giving this the same coding if it is the same situation.
Would you give this same installation a C3 if you had done the EICR without knowing the back story?
Don't let your emotions change your EICR codings, you need to remain impartial.
You aren't carrying the can for testing someone else's board change, you're not certifying it or accepting any liability for it.
You aren't even reporting on someone else's board change, you are merely reporting on the installations suitability for continued use.
I would explain to the customer what I have found and what problems there are and then discuss with them any work which needs to be done or could be done to improve things.
There are people on here who have been in the trade way longer than I , but I have noticed over my time that pretty much no 2 sparks do a PIR / EICR the same.
I reckon we could send 5 sparks to the same old house and we would get 5 different lot of findings and 5 very different lots of recommendations / Codes
Everyone is missing the point! A CU change is notifiable. Do the EICR , note any discrepancies and send the forms to Building Control with a covering letter and let them sort it out.
Don't rely on the trade body you are registered with to do the notification.Meanwhile tell the agents/landlords what you recommend to put the installation right.
SAFETY COMES FIRST, YOU HAVE A PRIMARY DUTY OF CARE WHICH OVERRIDES EVERYTHING
I don't think anyone is missing the point. We know the CU has been changed at some point, maybe as long as 5 years ago. We also know there may never have been any paperwork issued.
An EICR is to determine if an installation is safe for continued use. You have stated this yourself (in bold). Whether the installation of the CCU had been notified is irrelevant.
All you can do is comment on the current installation's condition, and if required apply codes and/or make recommendations based on improving the safety for continued use. The inspector is not there to police or do anything about it.
They wouldn't. But they might be interested in un-notified notifiable works.
In my experience they have little interest in electrical work , how ever they can hold onto a building competition certificate until they get the part p notification. where this comes from or whom it comes from they couldn't give a rats
If you C2 all RCD boards then dual RCD boards will be C2 as well , which as you say we would be C2ing a lot of fairly new builds
Not sure any would give a board with an RCD main switch a C2, unless it was faulty.
Thanks for the advice all, have decided the board will warrant a C3 and have sent a covering email to landlord/agent informing them of the report. I have also let them know that the EICR is not a replacement for an EIC and they may still need to provide this in future. Have quoted to upgrade to RCBO/SPD but I'm not holding out much hope looking at the rest of the flat!
This doesn’t warrant a C2
Going by your logic most consumer units I test I’d have to give a C2 as most aren’t full RCBO with SPD
With respect, I never said it would be a C2 purely based on it having a single RCD, but because it had a single RCD installed recently. I accept that I was wrong with this, and that the age of installation is irrelevant, but I still maintain it shouldn't have been installed that way.
Not at all, my point was that a single RCD is no longer compliant. A dual RCD is still compliant so it wouldn't warrant any kind of remark at all. Not that I like fitting them anymore when RCBOs are so much better.
Remind me again why it's not compliant and is that a statutory reg??
BS7671 314.1 and 531.3.2
None of BS7671 is statutory but it is still what we are required to follow - are you suggesting it's compliant right now to fit a single RCD consumer unit feeding one house/flat? Happy to be proved wrong but I'm fairly sure that's not the case?
Not sure 314.1 says not to use them or 531.3.2. Can you be more specific.
Remember in the new edition to be aware of the words should & shall.
There are no should's in the regs I quoted, only shalls...
Your right on both counts but your still wrong with your classification of the fault and nowhere does it say not to use them. In the right application they're fine. Unless your going to go round the tenants property and workout the earth leakage from all their appliances but even then it would be a C3 as it's only a nuisance. In other areas a board with an RCD main switch is the right choice. On an EICR we can put notes along with our classifications which should be done in a case like this. Yes they are all shalls as in divide circuits & minimise hazards but it still leaves it open so we can choose the best protective devices for what we are installing and at the time that was the best way so it's still a C3 with advice. RCD main switches are fine if that's what's required.
I don't think you've fully read my posts. I now accept that it is a code 3, and under normal circumstances that is absolutely what I would code a single RCD board. The reason I thought this one might be considered different is because it is clearly a new board (amendment 3 compliant) and therefore was installed at a time when Split Load was required at a minimum in this kind of installation. You say 'at the time this was the best way', but in this instance it definitely wasn't.
531.3.2 says, in essence, that you shall limit the risk of unwanted tripping.
Fitting a single RCD to protect a whole installation does not limit the risk of unwanted tripping. Therfore a single RCD protecting a whole installation is not fully compliant with the current edition of BS7671.
Measuring earth leakage is not relevant, that is only relevant to actual unwanted tripping, we are not concerned with that, we are concerned with limiting the risk of unwanted tripping.
Regardless of what the actual earth leakage is at any one time there is always a risk of unwanted tripping due to it changing.
Yes it is a C3, but that just proves that it is not compliant!
C3 is given to items which do not comply, do not present a potential or immediate danger, but can be improved for safety.
A C3 is not given to things which comply!
Reply to Landlord's EICR query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Hi, I have just had an EICR carried out and it has comeback with a few C2s. The only one I disagree with is the electrician raised as a C2 the...