I'm doing my 2395 practical assessment this week and I'm looking through my condition report inspection schedule.

in the case I come up against a low ( < than 1 mohm ) value on mega ohms while completing a IR test which box in the inspection schedule should I code this fault struggling to find a box which relates to it.

thanks in advance
 
A low IR reading would not be noted in the schedule of inspections as it is not something for which you can inspect.
The low IR reading would show up in the schedule of test results as it is part of the electrical testing you do.
Then on the schedule of test results you can put a reference number relating to the observation you make and the coding you apply.
 
  • Like
Reactions: 1 person