A potential customer of ours was asking about having more power made available. Just now it is just a casual request and it looks like they want 9-10 * 32A TPN supplies so, say, 315A total. We can get that much easily from the bus-bar chamber around 100m away but from a moment on an on-line calculator:
  • I am not relishing the prospect of wrangling 240mm cable in to a suitable MCCB board even with professional help.
  • Maybe better to put in two 160A sub-mains and then 70mm and a pair of 250A MCB boards?
  • Or three 100/125A supplies on 35/50mm to 125A boards?
Just to gather thoughts should it ever get to the stage of actually designing and costing it.

TL;DR How much parallelisation is sensible?
 
Last edited:
240mm seems a lot bigger than necessary for 315A 100m run.
It does seem a bit big, both Doncaster and Elan calculators give it though:

However, data sheet for Prysmian would suggest 150mm in duct is good for 315A.
 
It does seem a bit big, both Doncaster and Elan calculators give it though:

However, data sheet for Prysmian would suggest 150mm in duct is good for 315A.
It's all down to the installation method I suppose. For some reason I thought because of the mention of a bus-bar chamber it would be on cable tray🤨🤨🤨.
 
It's all down to the installation method I suppose. For some reason I thought because of the mention of a bus-bar chamber it would be on cable tray🤨🤨🤨.
It can go through part of the building on tray/ladder, but probably at least a section of it to 30-40m would go underground in duct.

Just now I am thinking that 2 * 160A 70mm supplies (with 35mm CPC added in parallel to armour) would fit the bill, meeting 5s disconnect on the cable to 100m or so and also good selectivity with both main fuses and MCBs.

Still to find out what they actually want or if they are willing to pay for it! Having said that, the annual bill for power is likely to be far more than the installation costs...
 

Reply to 315A sub-main options in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We are looking for a distribution board to provide 3 * 160A three-phase feeds, but they are basically redundant supply path options so max total...
Replies
4
Views
326
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Good morning all, long time reader first time post so looking for some help I’m qualified as an electrician but haven’t worked as a sparky for...
Replies
5
Views
2K
Hi All, I’m after some advice. I’ll cut to the chase but I can give more detail if needed. A 400A sub main supply needs to be ran 100m, a pretty...
Replies
5
Views
2K
Hi guys, I'm working in a new role which requires me to size SWA cable to feed sub boards which in turn supply EV chargers. I noticed on the jobs...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock