oh dear. BW glands sunbathing
Discuss 52 static caravans. what a HOOK UP in the UK Electrical Forum area at ElectriciansForums.net
bad idea if the glands are BW and corroded, esp if they are as bad at the supply end of the 16mm.unless you can prove it is TNS it should be a TT supply and using the armour cpc just to protect the cable so 16mm is good, most places only have 10mm supplying multiple outlets.
dont you mean a tin house on wheels .a little house on the prairies.Static caravan? oh... you mean "Luxury Holiday Home"
And are tenants still aliveMy site was 4mm swa to maybe 5 or 6 hook ups in a ring formation. Using a 3rd core for earth.
Place was extended and partial rewrite of old site as above a couple of years before I started.
Big local firm did it, but got the colours wrong. Ie, black for N, grey with earth sleeve brown for L
They were also connecting the vans with 1.5mm artic flex, not 2.5 as advised by the manufacturers. And some that had extras such as a washing machine or dishwasher were overloading the 16A mcb..... The old electrician they had was upping the breaker to a 20 without upgrading the flex size.
It was never the factory fitted appliances causing a problem... always the multitude of plug in heaters the owners brought in.
It's TT
bad idea if the glands are BW and corroded, esp if they are as bad at the supply end of the 16mm.