sambotc

Do you carry out AC IR tests with generation meter (elster) connected ie from inverter to disconnected conductors at the board, or will this damage the meter? I've been linking it out but apart from the test not being true to the installation it can be a pig if the meter is in an awkward spot!

Also IR testing on the DC side, what test voltage do you use? 1000v is the max rating on the DC cable, but 500v is sometimes less than the string voltage? Do you carry this test out with the inverter connected but off?

Sorry, being fairly new to the electrical side, IR testing always gets me worried i'm going to damage something!

Thanks in advance

Sam
 
Last edited by a moderator:
Either link out the meter or test L-E and N-E - you shouldn't damage the meter testing L-N with it in the circuit but it will give you a dodgy reading.

I IR test the DC side with the inverter disconnected. If my string voltage is over 500v then I test at 1000v, as long as the cables/panels are rated to handle it (as far as I am aware, they all are). For string voltages under 500v, I test at 500v but for no other reason than I am a big girls blouse and don't want to damage those lovely expensive panels. Yeah, I know, they can take 1000v.....
 
It's in the back of the DTI guide Appendix C table 1 if testing + and - shorted together to E then 0.5MOhms at 500V and 1MOhm at 1000V. Test voltage varies if testing + to E and - to E separately but you're governed by your tester.
 
It's in the back of the DTI guide Appendix C table 1 if testing + and - shorted together to E then 0.5MOhms at 500V and 1MOhm at 1000V. Test voltage varies if testing + to E and - to E separately but you're governed by your tester.

Those minimum values are from the old 16th Edition regs - so you may want to cosnider the 17th edition values which are double!
 

Reply to A couple of IR testing questions in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
622
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
655
Hi, I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR. I know you have to do one 1st fix at 500V...
Replies
6
Views
2K
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
746
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
770

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock