Hi all
Recently changed a consumer unit , adding new radial, bonding etc for my initial assessment, IR tested everything initially and before been terminated in new board, all readings ok.
I'm sure I've read that if it is a new installation that the board as a whole need testing?

My question is how can you test the whole installation when it is a wylex split board with 2 rcd's as the 500v could damage them?

Thanks in advance for your comments
 
Hi all
Recently changed a consumer unit , adding new radial, bonding etc for my initial assessment, IR tested everything initially and before been terminated in new board, all readings ok.
I'm sure I've read that if it is a new installation that the board as a whole need testing?

My question is how can you test the whole installation when it is a wylex split board with 2 rcd's as the 500v could damage them?

Thanks in advance for your comments

Always been told, (and agree with), that IR testing is done after termination of all conductors, accessories screwed on etc. etc.

You might damage or tighten down on a conductor when terminating and you wouldn't know.:)

As for the testing,

If you don't want to by-pass RCDs and test whole board,

Loads removed, MCBs off, outgoing side of each MCB to neutral bar/s and then to earth bar/s. Test between neutral bar/s and earth bar/s. Job done.
 

Reply to Advice needed; insulation resistance test on dual rcd board in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
578
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
586
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
826
Hello, I’ve got my AM2S coming up and I’ve been revising like mad but I’m stuck on something. I’ve read that it’s a 3 phase board with just...
Replies
11
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock