Recently changed a consumer unit , adding new radial, bonding etc for my initial assessment, IR tested everything initially and before been terminated in new board, all readings ok.
I'm sure I've read that if it is a new installation that the board as a whole need testing?
My question is how can you test the whole installation when it is a wylex split board with 2 rcd's as the 500v could damage them?
Thanks in advance for your comments
Hi all
Always been told, (and agree with), that IR testing is done after termination of all conductors, accessories screwed on etc. etc.
You might damage or tighten down on a conductor when terminating and you wouldn't know.:)
As for the testing,
If you don't want to by-pass RCDs and test whole board,
Loads removed, MCBs off, outgoing side of each MCB to neutral bar/s and then to earth bar/s. Test between neutral bar/s and earth bar/s. Job done.
Reply to Advice needed; insulation resistance test on dual rcd board in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Hello, I’ve got my AM2S coming up and I’ve been revising like mad but I’m stuck on something. I’ve read that it’s a 3 phase board with just...