1,261
Morning all,

I’m scratching my head with this and granted I don’t do a lot of commercial work. Hence I thought I’d ask.

Setup is a pub with a 3ph supply and it’s TT

So it goes

Incoming head - 3 x 100a cutout

Meter

3 pole isolator for L1, L2 & L3

L1 to single phase into plastic DB

L2 to single phase into plastic DB

L3 to single phase into plastic DB

Neutral into a Henley then to each single phase DB

However my understanding is that with a TT system it must be a 4 pole (TP&N) isolator? Only TNS & TNCS don’t need to have the neutral isolated.

Is there any reason why a TT system would be able to have an exception? I’ve no previous paperwork to look at to see a reason why.

Advice appreciated before I go back to them to tell them they need a 4 pole isolator.
 
For a TN system the neutral is deemed at earth potential so there is no need to isolate it but this is not the case for TT so the isolator must also switch the neutral.
 
For a TN system the neutral is deemed at earth potential so there is no need to isolate it but this is not the case for TT so the isolator must also switch the neutral.
That was my understanding. But I can’t understand how this has been signed off and had previous EICRs if it is not done right.

Hence I was wondering if I was missing something.
 
Just had a good chat with NAPIT technical and they agree it should be neutral disconnect being a TT.

So I’ll go back and tell the isolator needs swapping out. 👍🏻
 
Indeed. And that's without mentioning the requirement for all pole RCD protection.
Intention is to fit a 100A 100ma Time delayed Type A TP&N isolator.

Picked up this MCG one today.

4C5BA772-DC31-4DDF-8F5F-12A1D8B3A422.jpeg
D61DC590-AB92-43D5-B3C8-62FCFF6BD84C.jpeg
 
All insulated DBs I wouldn't be putting in a main switch rcd just fit a four pole DNO style switch.
 

Reply to Advice regarding isolator for 3ph TT system in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
840
Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a...
Replies
1
Views
431
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
579
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock