Hi, has anyone out there had any experience of the performance of air source heat pumps.

I am looking to fit one at my place. We are not on mains gas so am looking to find a way to economically heat the house - we currently have LPG.

The manufacturers make all kinds of claims for COP but I was wondering if anyone has any real measured performance. We have a relatively new house with underfloor heating so it will operate at a reasonably low temperature.

Cheers
 
There is a thread from last year regarding the legitimacy of the claims of these systems which are often sold in warmer climates have a search around for it, i also watched a tv documentary regarding air source heat pumps in our climate and the programme didn't do the product any favours leaving may customers with massive bills as the imm' heater was the back-up if temp' weren't met by the heat pumps.
It brought up many other concerns too but il leave it to you to look into it deeper.
 
I've got six of them going into a new build cul-de-sac that I'm doing at the moment - have to say that I've calculated for 'flat out' loads as I too have some very big doubts, and it gets mighty cold down here on the Levels!
 
The Energy Saving Trust started a field trial in 2008 the results of which are due ... i would contact them or seek their input on the systems and until i hear about the conclusion ill remain sceptical due to what ive heard in the past.... i belive poor design or lack of user knowhow can play a big part as to their efficiency.
 
I have sold one, working well, also my neighbor has one that has been installed for over a year now, he did have teething troubles but that was install issues, but still cost a lot less that their oil system to run, both of these are Mitsubishi which if memory serves me correct have no back up heat source unlike most other systems.
If circumstances would allow it is what I would choose, and PV of course.

I hope this helps.
 
Specified and correctly sized ASHPs do perform as well as any conventional heating system. Unfortunately the bad press seems to surround them owing to both lack of understanding on how to operate the controls by the householder and more often than not a heating installer who does not understand the principles of their operation and has just slung them in.
COPs on data badges need to be scrutinised, look out for COPs being quoted at 7 deg c, put into a heat calculation using a regional average of say -3 and you will get the likely COP.
These units are not plug and play, you have to make sure the house is insulated adequately, the flow and return pipework have to be big enough to get the heat around and the emitters have to be correctly sized for circuit temps of around 40 - 45 deg c.
Have a read of some manufacturers data, e.g. Mitsubishi Ecodan, Dimplex, Hitachi and Daikin etc.
 
I have one installed on my house 9kw TCAP using existing radiators no buffer tank yet (Buffer being done in summer). I am on mains gas. Coped during this winter and i am missing a radiator.
 
I have one installed on my house 9kw TCAP using existing radiators no buffer tank yet (Buffer being done in summer). I am on mains gas. Coped during this winter and i am missing a radiator.


What size/age house is yours Jason? We put an 8kw into 105m2 house in 2005 (ours) and it failed miserably because we had a 12kw heat load.
 

Heat pumps work very well but only with careful design and installation.

Throwing one into a retrofit situation without considering the building structure and u values is a recipe for disaster . Heat losses of 50 W/m2 is preferable and look at what the heat pump is actually putting out at -3 or whatever your design temperature is. Panansonic T cap is a great unit as it maintains constant output down to -15. COP is important at this point too.

A two day course is not going to give you the heating engineer knowledge or experience that's needed for heating design at this level.
 
I assume it was 8kw @ 7 degrees, it was one of the first out in the UK, there wasn't any backup with it so when it failed we froze. The installers were supposed to know what they were doing but after freezing for 2 months I worked out our heat loss and discovered a massive mismatch. At the time nothing bigger than 8kw was being manufactured.
 
Thanks everyone, the heat loss calculations say that I need under 12kW. I am able to link it directly into my UFH manifolds so should not have any mismatch issues with a 12kW unit but I would really like to know what COP is genuinely achievable in the winter (based in the South West) to justify the replacement of my LPG boiler (A rated). As the house is so well insulated the heating is only used 6 months/yr max. as hot water is from wet solar panels which so far have not let us down in the summer. We also have a back boiler on our wood burner in the lounge which provides hot water as well.

Is a COP average of 3.0 possible?
 
Is a COP average of 3.0 possible?[/QUOTE said:
In my opinion, yes it is, many will tell you that it is not though.

When EST give out the specifics of their trials it would be helpful to understand which type of house is the best, which make of heatpump etc.

Just one small point, with your underfloor heating heatpumps work better with 100mm centers, as they run at lower temperatures, the lower they can run the higher the COP.

The standard for underfloor heating is 150mm, do you know what you have?
 
Recently spoke to a couple loacal authority tennants who have had them fitted 6 months or so, they reckon they have cut there electricity bills in half literally, possibly by as much as 2/3rds, this is compared to storage heating. these were mitsubishi systems.
 
Earthstore, yes we are at 150mm centres but we have 100mm of extratherm underneath the UFH with all external walls having 140mm of insulation and 240mm on 1st floor ceilings.

When achieving an average of 3.0 with the COP what is the flow water temp?
 
I am not a total expert on this, but I do have an understanding and some knowledge,
The room temp you are trying to achieve is around 20 degrees, so the lower temp you can run a heatpump the better really,
If I remember correctly 45 to 50 degrees, a heatpump can rack it up to 60-65 but the COP drops like a stone.

By the sounds of you insulation, your house will be ideal, do you have PV, as that would help to reduce your running costs also, daylight hours only of course.
 
The house sounds ideal for a heat pump. How many square meters is it? I guess the heat loss would be something in the region of 50W/m2 so 160m2 house would need a 8kW heat pump. Do not add in the hot water load as it is usual to heat the water first then switch over to heating. A heat pump works better if it operates on a 24/7 basis with set back temperatures at night and in the day if you are out. Higher COPs will be achieved operating like this.
 
Last edited by a moderator:
Just to add, heatpumps run better on longer cycles, rather than stop start, this is why you may have heard of "buffer tanks",
these help a pump to cycle for longer, they are not always necessary, it is all down to good system design and install.
There again that is the difference between an average PV system and an excellent performing one.
 
Agreed earth store and we try to fit a buffer if the customer will agree whether the manufacturer specifies or not.

Dimplex do a combined unvented cylinder with buffer that is a convenient way of installing it.

Bad installs have done a lot of damage for heat pumps and this can only get worse if misguided sales and marketing companies get involved as the RHI looms. Bull***t sales techniques and sell at all costs is not the right approach. We walk away from a job if the heat pump won't work for that particular application. Would a salesman on commission only?
 
I believe it depends on the size of the system, Ie if it is a large house with excellent insulation, then only a small buffer tank would be required,(as there is plenty of fluid in the wet system) but if it is a small house with poor insulation then a larger buffer tank would be reqd, heatpumps also work on return temperature, so this can effect the cycling effect.
As mentioned, it is all down to system design, not just buy one and connect it up.
I may stand corrected on all of this though.
 
I have a 450 litre thermal store of which about half would be a buffer looking at the take-off point for the underfloor heating along with over 1km of UFH pipe so I would imagine I would be OK there. So the critical issue to me is what average COP am Ilikely to achieve with say a 12kW unit running 50ËšC flow and 45ËšC return temperature at a flow rate of about 2m3/hr over the winter months (unlikely to see any use May to September)??
 
Wiklipedia: Air Source Heat Pumps

Air source heat pumps - Wikipedia, the free encyclopedia

"Efficiency Ratings" / "Risks & Precautions".

Air source heat pump efficiency is measured by the "Coefficient Of Performance".
In very mild weather, the COP of an ASHP can approach or exceed 4.
However, on a cold winters day, as ambient temperatures reduce more work is required to move the same amount of heat indoors.
Heat pump performance is limited by the Carnot cycle and approaches 1.0 as the outdoor-to-indoor temperature difference increases.
In cold weather ASHP's become progressively more inefficient consuming more electricity as ambient air temperatures reduce.
At this point you'd realistically want to turn your ASHP system off and turn on a secondary supplementary heating system like a gas condensing boiler to heat your home cheaply and effectively.
People conventionally install ASHP's in locations where natural gas mains dont exist.
If an inexpensive, economic, supplementary heating alternative doesn't exist, you are lumbered with significantly increased electricity bills over periods of sustained cold weather.
Those that dont get very high ASHP electricity bills have systems installed in extremely well insulated houses, with low heating requirements.

Daikin Altherma:

Daikin Altherma air-to-water heat pumps are currently amongst the most efficient on the market with average COPs between 3 and 5.

www.daikinac.com/content/residential/whole-house/daikin-altherma/#energy-efficiency
 
Last edited:
I have some comparison test results from the Swedish Energy Test Centre but have no idea how to attach the document to a forum.

If you have contributed to this thread you can email me and I will send you a copy.

Beware the Daikin high temperature unit as we are told it does NOT qualify for the RHI.
 
Insulation seams to be the key before considering any heating system? I too haven't heard good things about this type of heating.

I had a customer that was convinced to go with a system by a renewables company, mainly because they would get financial help towards the cost. The house wasn't insulated and after finishing the work the renewable company accepted the house was also too large for the system and would never work properly!

Wish I'd seen the program Darkwood mentioned. Also looking forward to seeing the results from the EST :)
 
Heat pumps work very well if they are designed correctly and installed correctly.
Not all houses are suitable for heat pumps. Mine has been on since November on radiators that are oversized. Average temperature running central heating is 30 degree, jumps to 42 when weather is cold. Average temperature in house 22 all day and night. With my dual fuel discount my supplier owes me money. I'm on mains gas.
 
hi just been hooking up 2 x air to water unit working with thermal store on a barn conversion.

1st unit is main load with second unit as a slave. finished wiring last night 1st unit kicked in & ran whole system up without second unit cutting in.

speaking with the guy who supplied units they like to run lazy unlike a combi boiler you run hard.

they have 2 immersion back up's on cylinder aswell.

have 40loops of underfloor heating on system over 4 mainfolds.

looks good will get details & post
 

Reply to Air source heat pumps in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

My customer wants to be able to switch his heat pump (3.5kW) for his swimming pool on and off remotely, he also wants to be able to set times for...
Replies
8
Views
684
Hi, need more advise as getting two different views from electricians. Ty Detached double garage 10m from house, split equally into garden room...
Replies
3
Views
217
Hi, I have a Beko DHR73431W heat pump tumble dryer that isn't heating. I'm thinking its beyond economic repair as I think the compressor has gone...
Replies
0
Views
560
Hi, I recently moved into a house with electric storage heaters and am looking to replace them with electric radiators. Gas and oil are not viable...
Replies
7
Views
581
We have just completed a self build, and heating system is Air Source Heat Pump, unvented HW cylinder, Buffet Tank, all Vaillant equipment. The...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock