The type 1 SPD at source really only applies to LPS-equipped systems or ones with long overhead feed cables. Having a type 2 device is fine, so long as it is rated for the matching OCPD (if that is DNO fuse or separate MCB)

I suspect the NIC inspector is just following the "no mixed manufacture" aspect to the letter, which is kind of irrelevant for the outside DIN enclosure. But more importantly if the company making them certifies they are suitable for any CU subject to the matching MCB brand being used then they are taking responsibility for the overall design and you don't have to.
 
Last edited:
At the CEF 18th AM2 talk when mentioning SPD the guy said smoke alarms are not "safety systems" but as usual with no detail or justification for that point.

While there may be situations with a full CU where an overall SPD is not practical to fit for new alarms, in those cases you could just get the 10 year battery / wireless ones instead. If replacing existing alarm modules then you could argue it is not a new circuit so updated regs don't apply.

If it were a new hard-wired alarm I personally don't see how you could honestly say it is not for safety and so protection is optional.
 
At the CEF 18th AM2 talk when mentioning SPD the guy said smoke alarms are not "safety systems" but as usual with no detail or justification for that point.
Given that smoke alarms come under BS5839 part 6 why would they not be a "safety system" I think the guy really needs to clarify his comment as they are also a requirement of the building regs
 
I don't know, I wasn't there. The gaffer was the one who went around with the inspector. He couldn't see what the issue was, it's a Din module in an empty Din enclosure. Seems fine to me also, I've provided MCB protection, the correct size earth conductor and kept the cables as short as practicable.

If an inspector raises an issue, but can't give a reason for doing so (along with supporting evidence), I'd be inclined to think they were in the wrong job.
 
If an inspector raises an issue, but can't give a reason for doing so (along with supporting evidence), I'd be inclined to think they were in the wrong job.
A previous inspection I was picked up for not putting brown sleeving on the black interconnect wire on smoke alarms, even though all the NICEIC guides tell you to leave it unsleeved as it is an ELV control signal wire not mains switched live!
 
At the CEF 18th AM2 talk when mentioning SPD the guy said smoke alarms are not "safety systems" but as usual with no detail or justification for that point.

While there may be situations with a full CU where an overall SPD is not practical to fit for new alarms, in those cases you could just get the 10 year battery / wireless ones instead. If replacing existing alarm modules then you could argue it is not a new circuit so updated regs don't apply.

If it were a new hard-wired alarm I personally don't see how you could honestly say it is not for safety and so protection is optional.
Screenshot_20220821-131903_Drive.jpg

I would advise they actually read BS7671; verbatim from 18th Amd2
 
As for old boards you'll probably find the Wylex REC2SPD (main switch and SPD in a self contained unit) used to afford type 2 protection of the installation. It could be argued that as it located "at source" that it should be a type 1 but you generally see those on LPS installations, See the BS EN 62305 series.
Thank you for bringing this to my attention, I hadn't seen this before.
(In my view Type 1 would be overkill unless it was an overhead supply that is likely to be directly hit by lightening.)

EDIT Mind you at £122 + vat that's 2/3 of the cost of changing the board to a Fusebox SPD board with RCBO's anyway.
 
Last edited:
Its getting crazy, as now all rentals need smoke detectors and to fit the new detectors (New circuit or alteration of lighting circuit) we need to install SPD, that's going to add £100 + to the job just on materials. the clients/landlord are going to think we are taking the ----. as we know most landlords are tighter than a ducks .......,
 

Reply to Amd2 SPD on smoke alarms in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
353
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
544
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
946
Need advice please, I've been reading alot on spds and came across this, please read the picture I have posted, I am querying "equipment" if the...
Replies
1
Views
1K
Hi all! This weekend we have an offer on 8 of our most popular Smoke, Heat & CO alarms from trusted brands! Don't wait too long as these offers...
Replies
0
Views
386

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock