H

haden

Got called to a house the other day RCD trips when switcing on the kitchen light only problem is that they have a split board with one RCD that protects sockets, shower and cooker. The lights up and down and smokealarm are not protected by any RCD
I changed the light switch and it has improved a bit but it is now an intermitent fault as oppsed to everytime you switched the light on
I have done insulation test between circuits and all results are fine
Anyone come across this before all help much appreciated
 
Possibly an intermittent neutral fault between the lighting circuit and one of the RCD protected circuits. Would advise you to do some IR testing.
 
i'd test the RCD first, including a ramp test and check all connections in the CU.
 
Insulation test all the circuits, its a bit head numbing at first time you come across it but a crushed cable on a non-related circuit can effect rcd's.... i had a crushed non rcd protected lighting that when loaded would trip the rcd even though it was totally seperate .... i have heard a few similar stories since the intro of 16th edition where only sockets usually had cover but its where id be looking... ask if any recent wor has been done ....floorboards up etc walls drilled?
 
Come across this before, is the Kitchen light a florry , if so then it can sometimes effect an RCD on another circuit , some RCDs have a loss off Neutral sensing wire to overcome it ( earth wire)
 
Ive done the rcd test and it passes also ramp test all fine the lights are fed from the living room light to the switch and then to the pendant and on to the flory light so ray your point is of interest thanks the light does stay on all neutrals in correct bars and done ir test between cpc and live of each circuit and the neutrals but not individual will do this and suggest replacing the florry thanks again all for the replies
 

Reply to An interesting RCD problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
843
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
848
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
968

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock