watts where stated60w x 3
Ib design current1.30
In device rating and typeB6 MCB
BS 60898
Reference method

METHOD
B
Ambient
temp in ◦c
40◦c
Cable type/
insulation
90◦c
Thermo
setting
Single core non sheathed cables
Ca ambient factor0.91
Cg grouping factor0.80
Length in meters12.5 METERS
Max volt drop6.9
mV/A/m max31
Size selected mm21.5MM²
It3.41
Iz(must be larger than In)0.61
Actual voltage drop0.27V
Max disc time0.4
ACTUAL Zs0.18
Max Zs as bs76710.35
 
@Charles Lill , I've moved this post into your existing thread. Please don't post questions that are all related to the same thing in different threads.


Regards

SC
 
watts where stated60w x 3 180w
Ib design current1.30 0.78A
In device rating and typeB6 MCB B6 RCBO 61009
BS 60898
Reference method
METHOD Method B
B
Ambient
temp in ◦c
40◦c 40c
Cable type/
insulation
90◦c
Thermo 90c T/S single core
setting
Single core non sheathed cables
Ca ambient factor0.91 0.91
Cg grouping factor0.80 0.80
Length in meters12.5 METERS 12.5
Max volt drop6.9 6.9
mV/A/m max31 31
Size selected mm21.5MM² 1.5mm2
It3.41 8.24
Iz(must be larger than In)0.61 23A
Actual voltage drop0.27V 0.3v
Max disc time0.4 0.4s
ACTUAL Zs0.18 0.497 round it off to 5 ( using a Ze of 0.11 )
Max Zs as bs76710.35 7.28 x 0.8 = 5.82
Done it red for you
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
any guidance on this
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
3

Thread Tags

Tags Tags
guidance

Advert

Thread statistics

Created
Charles Lill,
Last reply from
JAWS,
Replies
3
Views
129

Advert