Hi guys after some advice. Been called to job where the house has been renevated and rewired about a year ago and put in some addition lights and sockets. There is a 10mm Earth wire from the MET which I'm told is going to the incoming gas pipe under the floor but is not accessible and there is no bond to the water which is plastic into the house then copper from there. The water is not accessible at the incoming position as the new kitchen has been built around it. Can I bond the both of the services at the boiler position as this is the only place where they are easily accessible? Thanks in advance