I am looking for some help, could anyone out there please explain to me a borrowed netutral in very simple terms, as im struggling with getting my head around it?

Also test procedure to identify?

Solution to rectify when installing 17th ed dual RCD board?

Many thanks
 
The borrowed neutrals are as a result of the live in the “Down Lights” circuit feeding the live side of the stair head light. This light uses the neutral of the “UP Lights” circuit as its “return path” and as a result is not “electrically separate from that of every other final circuit”

Ideally you should wire the circuit properly which more than likely would mean changing the switching arrangements. Normally if a client is not prepared for the remedial then you just fit the lighting circuits on the same RCD and note on the EIC on existing installation section what you have done and why and advise that it should be changed.
 
Many thanks, this is much more clear than anything else I have found. Could you go into more depth on remedial works? And testing procedure?
 
To test for borrowed neutrals you need to IR between each neutral and the others, I disconnect one at a time and test between it and the neutral bar. As stated it's quite common to find it on stair well lighting. Remedial is generally a case of getting a live down from the upstair cct to the downstairs switch as there are usually just two strappers taken between the switches so replace the twin with a 3 core
 
switch on both lights remove downstairs neutral out of board if landing light stays on its a borrowed neutral - plus down stairs switch will have a bridge over instead of a strapper cable - to fix it remove the borrowed neutral more than likely from the bathroom light and replace it with a neutral from downstairs light or from the c/u.
 
Its an even bigger laugh when DIY charlie puts up some grotesque wall lights in his front room, and then works out that they need a neutral to work. So he quickly works out that the socket just above him in the bedroom will do, so he takes a live from the lights and a neutral from the sockets, and usually doesn't bother with an earth at all!:90:

Cheers..........Howard
 

Reply to Borrowed Neutral??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Replies
17
Views
2K
During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms...
Replies
58
Views
8K
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
648
Evening all. I did an EICR recently and then changed a consumer unit. As part of the EICR process I take off around 25% of all accessories to...
Replies
9
Views
2K
Just a thought guys in terms of RCBO’s and supplementary bonding. Obviously supplementary bonding isn’t required as long as a 17th / 18th...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock