I want to add lights up my stairs like this, never come across this before would wiring point to point be classed in a zone with it running on the stairs or will i need to bury it in conduit?

Thanks

Screenshot_20200111_113621_com.android.chrome.jpg
 
Aico 3000
Scolmore Electrical Products
This official sponsor may provide discounts for members
R

radiohead

Esteemed
Arms
Safe zones are only vertical or horizontal, you'd have to wire in earthed steel conduit or use an earthed sheathed cable to go point to point with low voltage (230v) lights. Or use extra LV lights from a transformer to go light to light not in a safe zone.
If you do lights like this it's worth thinking about how failed units would be replaced, often installs like this are done with no thought for how to access for repair when it goes wrong.
 
telectrix

telectrix

-
Mentor
Esteemed
Arms
I'd mount some 25mm x 16mm mini trunking up the side rail below where you have the lights, then a small chase vertical into each light.
 
S

smity

-
  • Thread Starter Thread Starter
  • #4
Safe zones are only vertical or horizontal, you'd have to wire in earthed steel conduit or use an earthed sheathed cable to go point to point with low voltage (230v) lights. Or use extra LV lights from a transformer to go light to light not in a safe zone.
If you do lights like this it's worth thinking about how failed units would be replaced, often installs like this are done with no thought for how to access for repair when it goes wrong.
Thanks mate,

I did think that would be the case but with the stairs being a horizontal surface i was hoping there may have been be away around it.

I will stick some conduit in, would galv flexible conduit cover mechanical protection?
Post automatically merged:

Or go down the 12v route 🤔
 
telectrix

telectrix

-
Mentor
Esteemed
Arms
my method is easier, cheaper, and cables are accessible. you can actually get decorative trunking and make a feature of it.
 
S

smity

-
  • Thread Starter Thread Starter
  • #6
my method is easier, cheaper, and cables are accessible. you can actually get decorative trunking and make a feature of it.
Thanks, i am rewiring the house so this wall is being plastered so i may as well bury it, ive got some 20mm conduit on the van so not a big deal to put that in 👍🏻
 
Wilko

Wilko

-
Esteemed
Arms
Hi - as far as I know - flexible conduit is not sufficient so that zones may be ignored.
 
R

radiohead

Esteemed
Arms
Any conduit used must be earthed and suitable for use as a cpc, as above, no flexible conduit I've used is suitable for use as a cpc. I'm not really sure how you could easily adapt steel conduit to this, an earthed sheathed cable would be better, there is a cable designed just for this ,to be used just like a buried T/E, the name escapes me now...ask your wholesaler.
Edit....It's listed as Shielded LSOH on the CEF website, and meets the requirements for a buried cable outside of a safe zone
 
Last edited:
darkwood

darkwood

Mod
Mentor
Esteemed
Arms
Interesting one, although regulations denote a vertical or horizontal plane I feel this is one given the skirting run could contend for a exception in future regulations, it is a obviously clear assumption to make a direct diagonal plane to wire such a set-up, why the regulations specify vertical and horizontal is to give recognisable zones on a open plan wall, this however could sit in it's own exception.
 
S

smity

-
  • Thread Starter Thread Starter
  • #12
Hi - as far as I know - flexible conduit is not sufficient so that zones may be ignored.
Thanks mate, thats what I thought 👍🏻
Post automatically merged:

Any conduit used must be earthed and suitable for use as a cpc, as above, no flexible conduit I've used is suitable for use as a cpc. I'm not really sure how you could easily adapt steel conduit to this, an earthed sheathed cable would be better, there is a cable designed just for this ,to be used just like a buried T/E, the name escapes me now...ask your wholesaler.
Edit....It's listed as Shielded LSOH on the CEF website, and meets the requirements for a buried cable outside of a safe zone
I agree it would take some messing about to bend it at each box, the cable you quoted looks much easier but not cheap and only sold in 100m drums. I will see if i can source is in smaller quantities.

Thanks 👍🏻
Post automatically merged:

Interesting one, although regulations denote a vertical or horizontal plane I feel this is one given the skirting run could contend for a exception in future regulations, it is a obviously clear assumption to make a direct diagonal plane to wire such a set-up, why the regulations specify vertical and horizontal is to give recognisable zones on a open plan wall, this however could sit in it's own exception.
This is what i was thinking but couldn't find anything relating to a staircase or diagonal plane... I usually work on commercial/industrial so was hoping someone could point me towards a reg saying i could go point to point but it seems there isn't one ☹
 