Discuss Calcs Check in the UK Electrical Forum area at ElectriciansForums.net
L
LankyWill
New to the designing part and want to make sure im correct.
Got a 10 t+e that i want to feed a garage submain. I have wired it to an adaptable box which im going to joint with armoured. The armoured will run about 2 meters in a duct buried in the ground to a depth of 0.8m. There is no bunching factor as its run on its own through the ceiling and down block work to exterior hole. It doest pass through insulation as such but the cavity is insulated with polystyrene balls. Here is my calcs so far:
It= 43A
Cg= 1- no grouping factor as its on its own
Ca=1 -30*ambient temperature
Cs=1 -not sure if i need soil res if it runs through a duct?
Cd= 1 -is my run long enough to add derating factor?
Ci= 0.88 - tables a bit confusing length in insulation? or length of cable run in insulation?
Cf= using 60898 so not applicable
Cc= 0.9 as it runs underground for 0.8m
Iz=34.056A
i can therefore use a 32A B type to protect this cable?
What should i do if the install is 80% t+e and 20% 3 core armoured?
way out. 10mm T/E ref method C is Iz = 65A. the little bit of cavity wall insulation can be ignored. 50A MCB is advised. what you need to consider is if it's PME and there are extraneous parts in the garage, then the cpc of that 10mm T/E is too small to serve as a bonding conductor.
There is no extraneous bonding needed as there is no pipework in garage, Its a tn-c-s installation so the 4mm earth inside the 10mm will be adequate for fault protection. I thought single core was 65A and multicore was 63A?
i stand corrected. 63A is as per table F5(i) in green osg. i read the wrong table.
Reply to Calcs Check in the UK Electrical Forum area at ElectriciansForums.net
not to sure on how to find the wats for the power cable calcs could anyone help me its for a ring with 3 Dubble sockets on DB05-3L2 cable size...
Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Hi everyone, I'm new here and was wondering if someone could help to get my college project calculations right. I'm about to start my 2nd year in...
7K
After my last post and having and having to re-learn some stuff can someone check and advise on a few things. Sorry if this is wrong don't hate...