Hi llandrillo you are talking about an RCBO it trips on overcurrent like an MCB and on earth fault like an RCD. Don't concentrate on earth leakage it could be an insulation fault on the final circuit
I suggest start from scratch R1+R2, IR, polarity, Zs then function of the RCBO
Once you are convinced final circuit is OK then look upstream
An up stream fault can cause tripping but the usual cause is one of the up stream breakers tripping, which I think you’d notice. Are there any inductive loads being switched up stream?
went back today, everything fine since i changed a few accessories and the most troublesome room which tripped daily hasn't tripped since i changed the RCBO from a type b Eaton Mem tripping at 21mA to a Type c crabtree tripping at 27mA, i didn't change any lamps or accessories in that room, its very strange that only four rooms are effected, also that the distribution circuit supplying each room is on a different phase, so no one phase has a problem there.
One thing i did find though is that there is a three phase lift upstream, big motor, might cause the trip.
Nothing apparent on a visual of the room malcolm, the building is a 12 month old travelodge, essentially in mint condition and a new build not a renovation of an old property, ccu's for the rooms are situated in service risers alongside every other service like HVAC controls ect ect, but there are 40 db's in this place, one per room and only these 4 are effected.
Surge suppression on the lift springs to mind, but a bit drastic if only 4 rooms are affected. These rooms wouldn’t happen to be near the lift motor room would they? Or possibly off the same branch feeder? Just ideas.
Either get the lift company in and put the ball in their court.
Otherwise look a surge suppression at the board involved, the suppression will have to be on the live side of the lift supply.
Suppression works both ways it can stop a spike coming back in to the system. Depending on where it’s fitted.
I'll look into that Tony, I was told this morning that they had an emergency evacuation about two weeks ago as there was an electrical burning smell coming from the floor in question, customers thought it was the lift, the lift company came out and said it wasnt the lift.
Reply to Can an upstream fault cause an RCBO to trip? in the Australia area at ElectriciansForums.net
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...