Hi, so I'm looking at changing my thermostat from a honeywell manual to a honeywell DT90E digital thermostat and I was wondering if you could help me with where the wires should go please. First picture is the wiring of my current thermostat and the second picture is the instructions for the new one I was hoping to buy. Thank you for any advice given, its much appreciated.
 

Attachments

  • 20210107_230251.jpg
    20210107_230251.jpg
    234.8 KB · Views: 30
  • Screenshot_20210107-231928_Drive.jpg
    Screenshot_20210107-231928_Drive.jpg
    206 KB · Views: 30
Probably 3a, but might depend where the wires at the other end have been connected.
 
be careful with 3a. that switcheds 240V to the boiler. not good if the boiler wants a 24V switch.
 
  • Agree
Reactions: Boiler Repairs
From the OP's question, I think we can assume they're not very knowledgeable on this subject, so I said 3a to keep things simple. When I first saw the question, I was expecting the new 'stat to need a neutral which wasn't present, but no such problem.
They're swapping one 'stat for another, not rewiring the whole thing. Nothing changes at the other end of the single T&E we can see, so 3a is a simple and sufficient answer. I could have said any of the diagrams except 3e.
 
  • Like
Reactions: James
you're right. I read it wrong. only saw the 230V feed, not the 24 -230.24V.
 
From the OP's question, I think we can assume they're not very knowledgeable on this subject, so I said 3a to keep things simple. When I first saw the question, I was expecting the new 'stat to need a neutral which wasn't present, but no such problem.
They're swapping one 'stat for another, not rewiring the whole thing. Nothing changes at the other end of the single T&E we can see, so 3a is a simple and sufficient answer. I could have said any of the diagrams except 3e.
Thank you for the advice. Would you be able to tell me what wire goes where please as I am a total novice when it comes to things like this. Thanks again
 
Connect the brown and blue of the existing wires to A and B of the new 'stat. Brown should go to A and blue to B, but it doesn't actually matter for the 'stat to work.
The grey outer sheath of the cable must enter the 'stat, and there shouldn't be any bare copper showing where the wires go into the terminals.
 
Connect the brown and blue of the existing wires to A and B of the new 'stat. Brown should go to A and blue to B, but it doesn't actually matter for the 'stat to work.
The grey outer sheath of the cable must enter the 'stat, and there shouldn't be any bare copper showing where the wires go into the terminals.
Thank you so much
 
  • Like
Reactions: DPG
Thank you so much
New thermostat all fitted and working
Connect the brown and blue of the existing wires to A and B of the new 'stat. Brown should go to A and blue to B, but it doesn't actually matter for the 'stat to work.
The grey outer sheath of the cable must enter the 'stat, and there shouldn't be any bare copper showing where the wires go into the terminals.
New thermostat fitted and working, thanks again for your help.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Changing honeywell thermostat
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
Earlybird,
Last reply from
brianmoooore,
Replies
10
Views
4,590

Advert